HOW DO A DISTANCE RELAY SENSES THE FAULTY ZONE.
Answers were Sorted based on User's Feedback
Answer / amit sharma
distance relay operates on the zone impedance. If impedance
seen by the relay in the zone is less than the rated imp.
then relay trips and the zone is isolated.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / d ramesh
Distances relay senses the faulty zone if impedance seen by
the relay is below the set value then it operates and
isolates the faulty zone.
z=v/i below the set, then operates
zone1= 80% of protected line
Zon2=100%protected line + 50%shortest line
Zon3= 100%protected line + 100% longest line.
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / sukhvinder
relay works is ratio of voltage over current.line is
divided into zones zone 1,2,3. zone1 is 80 per of line and
set for immediately trip for line
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / limbian
Distance Protection Relay senses the faulty Zone by
recieving signal from Voltage Transformer
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / j.kesavan
it is sense sending end receving end voltage relay trip
depending upon voltage.
| Is This Answer Correct ? | 5 Yes | 24 No |
If Neutral Grounding Resistor (GR) failed/shorted. Is it repairable.
what is the name for a meter/tester to measure the paint quality in electrical panel or wall?
how to calculate the magnetizing current of ct ( 800A/1A) for Relay 64
how can you calculate fault level ?
I AM DOIN MY 3RD YEAR IN ELECTRICAL ELECTRONICS. PLEASE SUGGEST WHAT DO I DO NEXT AFTER MY B.E? AND I WANT TO GET INTO ANY PSU IS DER ANY EXAMS PLASE SUGGEST EVEN THAT.
Why we use Delta connection in the secondary side of a High Voltage transformer?
Which is the best protection in case of shortcircut fuses or mccb ?
xlpe cable 4 core nuetral wire is small why ?
how can i find ct ratio of meter by seeing name plate of meter and how it should be used in MF calculation if it shows only-/1???
why compound generator is used in generating station?
Alternator couple to diesel engine why, Alternator couple to ac service motor with gear drive for 1500 rpm possible (yes or no) aim to low input power supply give to motor then high output power taken for alternator Please answer this question
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)