how to select cable size?
Answers were Sorted based on User's Feedback
Answer / itsme
1. find load.... 8kw shower
2. find current Power/voltage ie. 8000/230 =34 amps
3. Use next fuse size up from current...40amp fuse/breaker
4. select a size cable suitable to carry 40amps
5. Find length of run. ie 20 meters.
6. carry out volt drop calculation
design current (34amps) x Length of run (20 meters) x
millivolt drop per meter (7.83 mvolts/meter for 4 square
cable) >>> 34 x 20 x 0.00783 = 5.44 volt drop!
if volt drop exceeds 9.2 volts use bigger cable
| Is This Answer Correct ? | 23 Yes | 5 No |
Answer / peer
If we know power calculate I(current) then select Breaker
and choose cable according to that.
Ex: Power is 50KW 3Ph supply.
I=100A (Apprx)
Breaker size for the above is 4c.35 sqmm+1c 16sqmm
E.C.C.
| Is This Answer Correct ? | 20 Yes | 9 No |
Answer / vzvodator
See this program -
http://miroshko.kiev.ua/cablesel/wiresel_mini_en
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / iftekhar mahmud
Caterpillar generator produce (Two generators) 127*2=254 amp
at 11 kv .
What would be the cable size (XLPE) to supply 256 amp at 11
kv? Air or surrounding Temperature is 32 degree C. Cable
will go under ground at 2.5 feet depth. Group Rating Factors
is 3 cables. Clearance between cables is 7 cm. Soil
Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2
K.m/W
I would like to use 3 separate single core instead of using
3 core cable.
Some says I should use three separate single core 120RM cables.
Some says 70RM .some says 95.
I m totally confused.
Is there ant specific rule to determine cable size?
Ifte
My e mail address is ifte13@yahoo.com
Anyone please send me the answer to my e mail address,
i will be very glad.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / vijay shinde
it simple it should be select on how much current will
cable carry
| Is This Answer Correct ? | 6 Yes | 13 No |
Answer / ahmed bilal
for calculating cable load, you have to email me
aoabilal@gmail.com
| Is This Answer Correct ? | 4 Yes | 17 No |
Answer / ashutosh tiwari
according to kelvins economic choice of conductor size
formula is
total cost = (P1+p2*a)+p3*a
a>>>conductor size
| Is This Answer Correct ? | 14 Yes | 30 No |
which motor is used in watch..??????
30 kva ups may kitne output voltage hote h
WHAT IS THE SIGNIFICANCE OF VECTOR GROUPS IN TRANSFORMER? WHAT WILL BE EFFECT WHEN PHASE DISPLACEMENT CHANGES IN TRANSFORMER?
5 Answers ABB, Nissi Engineering Solution, NSL Sugars,
Wat will happen if R-phase of an alternator is connected to B- Phase of AMF panel fed from alternator
in india single phase is 230v and three phase is 440v but in other countries single phase is 110v and three phase is 380v why..?
how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263 Amp ?????????
Natural frequency of a system gives... 1) nature of transient 2) overshoot 3) oscillations 4) speed of response
Why generating power limited to 11kv?
Difference between EDO and MDO breakers?
if dc is better then ac...then why we are perfering ac over dc?eg:at home?
What are the minimum acceptable insulation resistances of insulation of underground cable suitable for 0.440kV,11kV, 33kV and 66kV?
generator(Deutz 550kv)is runing for 2 hours with load of 900 amp and then it goes in shutdown with alarm fault messege of speed fault although heirtz reading fixed at 50,what does that mean
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)