I have a question, I visit 01 site and face a problem,
there is 2.5 ton Air Con working, when air con compressor
is running at that time rectifier voltages are increasing
upto 290-295 v and rectifier is giving main high alarm
(rectifier is APC single phase, before starting compressor
rectifier voltages was 230v. when air con is going off
rectifier voltages are decreasing smoothly at its actual
voltages 230v.
Load on Genset phases is this: Red-13.5 amp AC (Air Con
load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp
AC (telecom system load),
Genset phase to phase and neutral to phase voltages are
also ok.
These are 10 sites having same system and same rectifier
APC brand at every site 02 genset are working but the
problem is same at all these 10 sites.
What will be the reason behind???
Neutral CT for 45MVA 132/11 KV YNd11 Transformer. NCT REF CLASS-PS or 5P20 with 20VA burden which is suitable.
when the PFR (POWER FACTOR REGULATOR)change a step to zero,one of the RCCB will triped off,is it the changing step of this PFR effect the RCCB?
When lag/lead/lag-lead compensation is employed?
What is min and max voltage between earth and neutral/phase if it perfect earthing?
37 Answers Epoch, ISS, ITC Infotech, L&T, Power Works, Statex, Sterlite, Wipro,
What is the lifetime of a Thyristor? Is there a recommended lifetime for thyristors after which they should be replaced?
in ONAN type transformer winding temperature is lower than oil temperature at evening time but morning winding temp is higher than oil temp what is the reason?
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases voltage A does not alter B decreases C increases D none of above
What is hysteresis losses?
What is the difference between earth and neutral
4 Answers ABB, Tamboli Engineers,
How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?
What is CRT (Contact Resistance Test) for Isolators or Dis- connector Switches? Why we performed it & whats the Testing procedure.
What is auto reclose system in Circuit breakers??