HOW VFD USED IN ENERGY SAVING
Answers were Sorted based on User's Feedback
Answer / suresh
VFD – variable frequency drive..
VFD is useful in energy saving because it reduces the
motor speed as demand decreases.When the speed is reduced
the power consumption Will also reduce because ,
Power = (speed)3 {cube of speed}
For example if the speed is reduced to 80% of the maximum
value the power consumed will be reduced by 50%
Power consumed = (0.8)3 = 0.512 = 51.2%
| Is This Answer Correct ? | 108 Yes | 8 No |
Answer / manoj patel
VFD drive controll speed of motor by varing its freq.
But at varing freq. it have to maintain V/F ratio
constant.So for reducing speed it have to reduce freq.but
its also maintain V/F ratio constant.So automatically its
voltage is reduced.
So powre is depends on V, I & PF. So its save energy..
| Is This Answer Correct ? | 30 Yes | 4 No |
Answer / rahul
Practically VFD helps to save enery in Variable torque
loads only like Fan , pump. With affinity laws Power
proportinal to cube of speed, so if speed is reduced you
will get energy saving by using this law.
For constant torque application , if your process speed is
not full RPM but less than that say 30 Hz , then energy
saving will be there by using VFD, as you are not required
to run the motor at full speed.
| Is This Answer Correct ? | 13 Yes | 2 No |
Answer / mashood
The real saving is observed when the VFD is used on input reference of temperature, pressure, differential pressure etc.,and this is more significant in case of Fans and Pumps, specially when we calculate the energy consumption over a certain period of time where different temperature and seasons are involved.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / tilak guruge
vfd is help to reduce the power consumption and saving the life time is motor and other related pats of the pump.basically vfd is control the motor speed and its give command to the motor as a demand
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / itc ltd, snacks ,haridwar
Drive function is power convert,one way to onother way(by
phase convertor)So improve the power factor,
| Is This Answer Correct ? | 24 Yes | 38 No |
what is the working principle of energy saver control panel. please give the complete calculation & theory.
How to calculate ant test the burden of Current transformer
sourse is 66 KV / 350 MVA, transfarmer is 1000 KVA 6.6 / 0.415 kv, iF fault is 28.75 MVA on 0.415 KV Bus then calculat the Transfarmer Impidance
why we use core type and shell type transformers?
What is ac and dc drive.
suppose a fan is running with phase and neutral. if its neural is touched to body. then fan get stopped. if this fan is connected to phase and ground supply..then why it runs?
why the field winding in dc motor is not short circuited eventhough dc supply is applied across the winding
What is Procedure the procedure to select CT's & PT's in 66kV and above substation
As we know diode work on both negative and positive but converting ac into DC we have to given a/c from negative of diode or positive side.please give me answer.
why select the 3 phase power supply system in electrical system.
Am using an electronic digital display to see the RPM of ABB ACS 550 drive, which is showing negative value when the motor & drive in stop mode but it is showing correct value during the run mode. can anyone help me out??
2 Answers Bala Power Solutions,
how to claculate the ups load in KVA pls give the if any fourmoul?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)