What happen if 1200KW/1500KVA alternator runs at no load
and high R.P.M.for one minute?
Answers were Sorted based on User's Feedback
Answer / dr.d.m.kothari
This will never happen because AVR and giverning
arrangement.Governor always control speed according to load.
| Is This Answer Correct ? | 9 Yes | 0 No |
If prime mover runs very high speed (without any control)
within a fraction of second rotor damaged and after that
Excitation system damaged.It will goes very dangerous
mode.So Never run Alternator without control.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / gurucharan singh
Generator loading & No load running has no effect its
paramaters, means generator run at no load as required.
Second part of question, generator are normally designed to
1.2 to 1.5 times of nominal speed to run for one minute
without any problem. Very generation system has a speed
controller & voltage controller which responce to these
condition within 1 to 2 seconds. I suggest interviwer shall
not confuse to candidate at interview.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
There are over speed and over voltage relays to
protect.Governor becomes helpless if there is sudden throw
off of load,then over speed relay of the governor shuts down
the prime mover.With AVR, voltage does not increase.However
generators are designed to withstand runaway speeds for
short periods. Bearings are first to get damaged under
prolonged high speeds.Governors can also be made not to
allow for undesired high speeds with the help of braking
systems, if they are employed.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
The above is applicable to hydro-generator
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / n r@jesh
D.G runs No load condition out put voltage will generated
high so, system protection will damaged
| Is This Answer Correct ? | 0 Yes | 1 No |
What are various impedence in any machine
2 Answers Engineers India Limited, NTPC,
what is relay multiplier
1 Answers Atomic Energy Commission, Bhel, Wipro,
what is corona effect?
39 Answers ABB, Genco, Wipro,
What is the diffrence between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?
resitance in ac=1.6*resistance in dc
why don't we use the generator as a motor? and what will happen?
How much energy save vfd if motor run on 50 Hz (full speed)
what is an rmu?its circuit diagram.functions
14 Answers CP Bangladesh, Emrill, NDPL,
What is mean by hot and cold loop testing?
3 measuring instrument for transformers?
Why DC Currents are not used in transformer?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)