What happen if 1200KW/1500KVA alternator runs at no load
and high R.P.M.for one minute?
Answers were Sorted based on User's Feedback
Answer / dr.d.m.kothari
This will never happen because AVR and giverning
arrangement.Governor always control speed according to load.
| Is This Answer Correct ? | 9 Yes | 0 No |
If prime mover runs very high speed (without any control)
within a fraction of second rotor damaged and after that
Excitation system damaged.It will goes very dangerous
mode.So Never run Alternator without control.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / gurucharan singh
Generator loading & No load running has no effect its
paramaters, means generator run at no load as required.
Second part of question, generator are normally designed to
1.2 to 1.5 times of nominal speed to run for one minute
without any problem. Very generation system has a speed
controller & voltage controller which responce to these
condition within 1 to 2 seconds. I suggest interviwer shall
not confuse to candidate at interview.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
There are over speed and over voltage relays to
protect.Governor becomes helpless if there is sudden throw
off of load,then over speed relay of the governor shuts down
the prime mover.With AVR, voltage does not increase.However
generators are designed to withstand runaway speeds for
short periods. Bearings are first to get damaged under
prolonged high speeds.Governors can also be made not to
allow for undesired high speeds with the help of braking
systems, if they are employed.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
The above is applicable to hydro-generator
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / n r@jesh
D.G runs No load condition out put voltage will generated
high so, system protection will damaged
| Is This Answer Correct ? | 0 Yes | 1 No |
Why consider motor rpm to select capacitor for motor
what is the difference between synchronous & asynchronous generators
is harmonic useful or it distort the alternating quantity?
What Is the Difference Between Lightening Spike and Lightening Arrester?
Where can I get CPWD electrical specifications & Shedule of rates? Please help me
can we transmit power with out cable if it is possible how it is possible.
when the rheostat kept in minimum to maximum position in motors what will happen?
I have an existing old MCCB. ABB Model SACE, the rating are: Ue = 660 volts, Iu =1250 Amps, 3 poles, Ith (max) =800 amps at 45 deg C. I need a circuit breaker for my 3 phase motors, 380 volts 60 hz. the supplier required the minimum ampacity of the breaker to be 911 amps. can i use this breaker with rating of Iu =1250 amps but Ith = 800amps maximum?
I AM COMPLETED DIPLOMA IN E.E.E. AS WELL AS B.TECH IN ANDHARPRADESH.. HOW I THE Certificate of competency as Electrical Supervisor.
What is the effect of using an underrated size cable to supply electrical power to a 3 phase ac electrical motor? What is the effect of using an overrated size cable for the same motor?
phase clearance between phase to phase and earth
which safety we have to take when we go for work?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)