How to calculate the current carrying capacity of
electrical cables
Answers were Sorted based on User's Feedback
Answer / ghanshyam kannaujiya
current carrying capacity of the conductor is depend on
size of cable and current density of used material of cable
conductor
current carring capacity= size of conductor/current density
of materils
| Is This Answer Correct ? | 159 Yes | 55 No |
Current carrying capacity = FLC / DF
To refer cable catelouge choose the cable sizes
-Derating factor (DF) =0.72
-Full load current (I)= P / (1.732 x V x P.F)
| Is This Answer Correct ? | 123 Yes | 40 No |
Answer / venkatesh a
For calculate the current carrying capacity.
First we should calculate the cross section area of the
conductor (sq.mm) and conductor material used in cable.
Each and every matals are having its own current carring
capacity. This table is avail at IS.
Current carring capacity may reduce by some other factors
like the cable length and insulation's heat withstandable
capacity.
| Is This Answer Correct ? | 101 Yes | 28 No |
Answer / lokesh.thota
There is no need to calculate ampacity of the cable it would
be provided by the manufacturer its self or else if you want
to calculate it by your self you should also know its
specific resistivity,working temp,core dia & insulation
thickness.
| Is This Answer Correct ? | 134 Yes | 81 No |
Answer / dipesh kumar
The current carrying capacity of a cable is called
Ampacity. For the porpose of the above calculation there
are some concepts that must be taken in consideration .
like Dia,Insulation material and thickness,type of conductor
(Copper/Aluminium),Resistivity and the working conditions.
For BETTER CONCEPT I advice the readors to please refer
the "Recommended Cable Sizes and their load capacity as per
IS:13947 & IEC 60947". Below given table can help you.
Rating Cu Al
10A 1.5MM2 1.5MM2
15A 2.5MM2 2.5MM2
20A 2.5MM2 4.0MM2
25A 4MM2 6MM2
| Is This Answer Correct ? | 89 Yes | 36 No |
Answer / t.raju goud
Actually current carrying capacity of the cable we can from
the manufacturer, But for the referance purpose I can give
some idea about current capacity of the cable.
So generally we are using two types of cable i.e,. copper &
Aluminium.
copper is the best conductor than the aluminium
At 1Sqmm copper conductor will Approx 2 amp in ground
At 1Sqmm copper conductor will Approx 2.4 amp in air
At 1Sqmm Aluminium conductor will Approx 1.2 amp in ground
At 1Sqmm Aluminium conductor will Approx 1.6 amp in air.
For example:
p=50kw
load current=87amps
So
for aluminum cable size(air)= load current/1.6
=87/1.2
=72.5
But In the market there is no availability for 72.5 Sqmm so
we can propose 70Sqmm or 95Sqmm.
This is the one of the best procedure for for cable
selection with using catelogues
| Is This Answer Correct ? | 81 Yes | 36 No |
Answer / arun reddy
It depends on many factors.
1. Material - Copper/ Aluminum
2. Voltage Class - Some volts to 765 KV
3. AC/ DC
4. Type of Insulation
5. Most Importantly - Cable Cross-section Area
Refer IEC-60183 for detailed guide
| Is This Answer Correct ? | 52 Yes | 19 No |
Answer / amit jain
Refer IEC 287.If you want me to calculate the same. i will
do it for you
| Is This Answer Correct ? | 35 Yes | 21 No |
Answer / abdul haseeb khattal
Well, First try to calculate the total load of the system.
For example total load is 1000KW. The current can be
calculated as P=1.732VICOS(PHI). Hence total current will
be 1732A by considering V=415volt, power factor=0.8.
Step2: To calculate the cable size
Vd = mV/L/A
where Vd= Allowable voltage drop which is normally 2.5
percentage to 4 percent.
L = Lenght of the cable from the source to feeder
A = Ampere rating
Let us consider L = 1000Meters
A = 1732A
Vd = 2.5 percentage of 415V as in U.A.E.
= 2.5*415/100 = 10.375
Use these value in the above formula
mV= Vd/L*A
= 10.375/1000*1732
= 0.005 volt
Refer to the cable catalogue in your region and find out
the current carrying capacity of the cable which will be
totally depend upon the atmospheric condition, in cold
place a smaller diameter of cable can carry larger current
and in hot areas the same size will carry lesser current.
In U.A.E. we are normally using 11x1c 630sqmm cable with
2500A incomer breaker. But cross check the voltage drop as
calculated above is within the limit of voltage drop of
these cables else you have to go to higher size of cable
untill the voltage drop met the design milli volt drop of
the cable.
| Is This Answer Correct ? | 16 Yes | 12 No |
Answer / himanshu
hi frnd.. what will u say for the given ques. if interviewer asked, How a manufacturer determines the current carrying capacity of electrical cables??
| Is This Answer Correct ? | 8 Yes | 5 No |
To prevent the mal operation of a differentially connected relay while energizing a transformer, the relay restraining coil is baised with (a)second harmonic current (b)fifth harmonic current (c)third harmonic current (d)seventh harmonic current
why do we use UPF watt meter in short circuit test of the transformer and LPF watt meter in open circuit test of the transformer
where AVR is connected in power plant.
7 Answers ABB, Saudi Red Bricks,
what is the difference between active power and reactive power and apparant power in practical as well as theoritical
what is units of resistance
why two point starter,three point starter, four point starter cannot be used for A.C machines?
What will happen if mains neutral and generator neutral shorted?
In a voltage-controlled current source A A current booster is never used B The load is always floated C A stiff current source drives the load D The load current equals Isc
What is YNyn Transformer? and what are the other types in this?
what is the exact direction of current? as we know current travels from higher potential to lower potential,so if we take battery +ve to -ve implies current direction is from positive terminal to negative terminal.,whereas electrons flow from negative to positive as they are attracted by positive ions.current will be the plow of charge but not flow of positive ions.please clarify my doubt friends.
Ammeter of 1 ohm resistance measure max 10 ohm to measure higher resistance from it
why it is in star to delta form of Synchrounus generator and delta to star form of Generator Transformer (or step up transformer)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)