Why size of HT cable is less then LT cable inspite of the
fact that voltage is higher in HT cable?
Answers were Sorted based on User's Feedback
size that is the cross sectional area of cable that is in
Sq mm. mainly depends on current carrying capacity of cable
and second on voltage if voltage increases than the
current decreases. so in HT that high tension above 1.1 Kv
current carring capacity decrease for transferring the same
amont of power. so is the size reduced . yes it has extra
insulation for this high voltage.
Is This Answer Correct ? | 37 Yes | 2 No |
Answer / rainy
Hirer the voltage the lower the current. And the lower the
voltage the lower the current. Say for instance if you were
feeding the high side of a transformer with 230kv and the
sec. side was 100kv usually the size of conductors would be
(high side 1 mill. and on the low side would be 2 mill.
wire size usually dual conductors to carry the load on the
low side.
Is This Answer Correct ? | 6 Yes | 14 No |
in thermal overload relay class 10A indicate what
Why the CT Secondary is rated as 5A generally?
which connection is safer series or parallel?usually which connection we prefer at home?
why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage from 33kv to 415v directly using single transformer.
12 Answers ABB, Adani, Central Electricals, Electrical, HCL,
What is GIS (Gas Insulated Switchgear)
hello freinds what is advantage and disadvantage of plc again dcs?
3 pahase 750kva Running 2 DG sets in 35 mints.525ampers. and 616 kw how much fuel consumption in Generator.what is the formula.
1 Answers Delite Systems Engineering,
what happens if DC earthing and AC earthings are shorted?
what is saturation kit?which use above 15 kw motors panel side.
A 11 KV motor is working. if the supplay is fail. what will happened with it's breaker? Trip / remain the same condition?
area control error
How to calculate cable size? How to O&m of vcb?