What happens if 25 Hz frequency is applied for 400/200,50 Hz
single phase Transformer.Will Voltage increase ?
Answers were Sorted based on User's Feedback
Answer / raji g
voltage will not increase obviously it will decrease because
the induced emf in the secondary winding the transformer is
directly proportional to the supply frequency.
Hence the voltage will reduce at the secondary winding
when will give the 25Hz.
But it is not advisable to give the 25Hz frequency to 50Hz
designed transformer.Because the transformer impedance
designed such that good efficiency at 50Hz only.
if u give the 25Hz the transformer winding may lead to get
over heat and may burn the windings due to the following reason
the reactacne(xl) of the transformer is direct proportional
to the supply frequency. so for reduced frequency the
impedance of winding will reduced and current will increased
to large level
Is This Answer Correct ? | 16 Yes | 1 No |
Answer / shahulsnfa
Obviously no. Voltage ratio remains same as designed. But the output supply frequency will be 25 Hz same as supply frequency...
Is This Answer Correct ? | 3 Yes | 8 No |
why we use REF and Differential Protection in one transformers?my doubt is both protections are operated in internal fault only.why we want to use 2 protections?please clarify.
what is main advantage if motor connected in star or delta?
HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED
send me all basic electrical question and answers
why we don't discuss power facter in dc?
what is the breaking capacity and making capacity of circuit breaker and how
what is difference between 2wire method and 4wire method of winding resistance testing of transformer?
As per the theory current doesn’t flows in Neutral, but practically it is not applicable, explain why?
In an ammeter used for measurement of current, what is the meaning of the representation of range as '0-50-300'?
What should be the amps for a MV fuses for transformer 630kVA 20(10)/0.4 kV
Two alternators say 1 & 2 are poised to parallel operation. But at the time of paralleing alternator 2 gets out of the system by tripping Earth fault relay. Please send me reply why this is happening?
what is electricity