Hod do u calculate cable size for underground laying and
the factors effecting/influencing it??
Answers were Sorted based on User's Feedback
Answer / abduljameel
Selection of cable size based on the following:
1.Load current
2.Length of the load from the source.
3.Cable laying area(underground,cable tray,area)
4.Permissible voltage drop.
Kindly refer cable manufacturer catalgue for selection
| Is This Answer Correct ? | 39 Yes | 7 No |
Answer / nitiyanandam
FOLLOWING EACTORS R CONSIDER TO SELLECTION OF CABLE
1.sellection of condutor ALU or CU
2.cable insulation PVC or XLPE
3.load current.
4.lenth of conductor.
5.voltage drop.
6.temperature.
7.apply voltage.
| Is This Answer Correct ? | 22 Yes | 4 No |
Answer / madhav
While other answers are general procedures for selection of
cable, underground cable laying is different, AFTER having
taken the above factors into consideration.
The laying of underground cable should also consider the
permissible conductor temperatures, ambient temperature,
number of cores and mode of laying (single cores or
multicores), etc. The maximum current carrying capacity
also varies with the type of cables and its insulation
properties.
Cable laying is also of several types. In case of single
core cables, they could either be close together or
seperated by one diameter of the cable. That could also
cause differences in current carrying capacities.
In general, for a loaded 5 core cable when laid in ground,
the derating factor could be 0.7 times the rated current
carrying capacity of the cable.
| Is This Answer Correct ? | 5 Yes | 5 No |
In case of laying of single core cables then trefoil
formation should be adopted. i.e. R Y and B phases should
be clamped with alluminium clamp only or Stainless steel
clamp to avoid induction.
Derating factors are also to be considered which depends on
the distance of cable laid from each other. If cables are
touching one another incase of multicore cables then
derating factor will be about 0.5 to 0.6 or so.
| Is This Answer Correct ? | 3 Yes | 3 No |
(1)For 3 No 1500 KVA transformer require on one single bus bar or need to be section through bus coupler means upto 3MVA.(2) 22KV Net work system as ring, How maney I/C required or 0ne I/C and one O/G.(3) What should be rating of VCB for 22 KV line.(4)Electrical/mechanical inter lock, why we need.
what is ups Paralleling? how is load sharing at that time ? what are the things we have to note that time?
CAN CU XLPE/PVC CABLE BE USED INPLACE OF LOW NOISE SCREENED CABLE? KINDLY GIVE REASONS
what is sevice settings for mccb?How can be it setted?
Compare jfet’s and mosfet’s.
Why alternators are designed at 0.8 pf lag?
what are the different types of transformers in present? which transformer is efficient?
Assume a condition such that two motors of rating 6.6kv,415v are connected to blower,so tell me which motor draw large current give appropriate reason?
why u r living from presentaly working.
How do u analyse protection fault when vcb tripping on load
How to take Transformer oil Break down voltage test?
What is the Current equation in series RLC circuits.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)