Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

Hod do u calculate cable size for underground laying and
the factors effecting/influencing it??

Answer Posted / william lobo.

In case of laying of single core cables then trefoil
formation should be adopted. i.e. R Y and B phases should
be clamped with alluminium clamp only or Stainless steel
clamp to avoid induction.

Derating factors are also to be considered which depends on
the distance of cable laid from each other. If cables are
touching one another incase of multicore cables then
derating factor will be about 0.5 to 0.6 or so.

Is This Answer Correct ?    3 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is the difference between Static and servo controlled voltage stablizer?

2160


what is the isolation transformer. what is the isolator?

2058


is ac supply can store

2088


what is the differebt between ac and dc fuse?

2321


How to calculate the multiplying factor for energy meter with ct ratio given

2007


what is interfacing in computer studies?

1755


Did RMU have ct and pt ?

1349


What if high voltage side circuit breaker of a ehv transformer instead of lvcb? Kindly elaborate.

1731


How is the connection of the tap changer on the HV side been made?

1955


1) why a dg set shows variation of power factor and load when synchronised with other dgs? 2)Why the load sharing is not become equal in all dgs?. 3)When a dg set will not run on auto start?

1986


i applied for the ap transco please forward the freqventley asked QA

1987


why servomotor motor? where i apply for best output?

2024


Importance of fault current in power transformers and how to monitor the same? How is it different from winding temperature?

1823


How can i calculate the Breaking capacity of molded case circuit breaker, is the breaking capacity of CB for Diesel generator shall be less than grid supply's breaker ?

2213


3- What is the target from Zero Impedance, Single Phase Imp., S/C Imp. and magnetic balance tests?

1842