What is In (current rating) shown on the MCCB? Is this full
load which can withstand by the circuit breaker
Answers were Sorted based on User's Feedback
Answer / chandra_edu
The current shown in mccb is like below
240/415v
9kA
20A
here 9ka means rated short circuit current when appears
during fault which mccb can withstand
and
20a is actual load current it can withsatnd
Is This Answer Correct ? | 15 Yes | 4 No |
Answer / devesh mishra
ln=200A means the full/maximum load current(200A) beyond which the MCCB trips due to overload.
9KA stands for the breaking capacity.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / manikandan
20a-MCCB rated current
9KA-MCCB Breaking capacity ahen short citcuit occour
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mrudang
20a = eithstand current by mccb
9ka = breaking capacity of mcb
Is This Answer Correct ? | 1 Yes | 1 No |
what are different types of alternator and discuss about the methods of cooling
16 Answers Bhel, Jindal, L&T, Nalco, Vedanta,
what is work of choke in tube light?
which cable is preferred PVC OR XLPE for voltage from 220V to 11 KV with proper justification
why transformer neutral and CT Secondary neutral is connected to earth?
where we use the SFU & FSU?
what will happen if the frequency supplied is more than the frequency of the instrument...?
Which factor decide the colour of the light emitted from a Led?
what is cable meggering formula for low voltage ?
hai iam arunkumar. i have applied for an section enginner in rrb. i want lat 5 years solved question papers. if u have please sedn it to arun30682@gmail.com
Why consumers are charged based on Kwh basis why not on Kvah basis.
what is the purpose of measuring % impedence?
1000 W bulb takes 4.16 Amps at 240 volt then what will be the KWH & if i am using 1000 W bulb at 180 Volt the amps will be 5.55 then what will be KWH????????????????