Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

What is In (current rating) shown on the MCCB? Is this full
load which can withstand by the circuit breaker

Answer Posted / devesh mishra

ln=200A means the full/maximum load current(200A) beyond which the MCCB trips due to overload.

9KA stands for the breaking capacity.

Is This Answer Correct ?    7 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how does ELR works? explain

2659


What is the gross weight to copper ratio in slip ring induction motor of 4000 HP,6.6 kv, 372amp, 992 rpm GE motor.

2347


What is dynamo function in DG sets and draw block diagram?

2020


dg started in plc mode and load taken later one battery terminal connection will be disconnected by loose connection what will happen for dg and shall we connect battery terminals while dg in load time?

2046


Define open loop control system.

1082


I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF

4013


State the other types of Air Conditioners?

2037


Why are the cores of large transformers built up of circular transactions ?

2002


what are problems caused by the pdu in rack server

1962


why r we using shell transformer for low voltage

1993


Define load factor?

1090


Which Class insulation is prefered for the sandwich Busducts ? Why?

2019


what is the reactance,capacitance & impedence electrical armoured & unarmored Cables.

2179


Will any motor burn if voltage provided is lesser than the rated voltage???? If yes, then how is speed control possible with voltage control

2146


WHAT IS AIR GAP VALUE IN MM FOR A 11KV BUSHING OF 11KV/440V DISTRIBUTION TRANSFORMER. AND AIR GAP VALUE OF 25 KV BUSHING OF AT TRANSFORMER OF 25 KV TRACTION. WHAT IS THE CALCULATION FOR THE AIR GAP PERMITTED FOR BUSHINGS AT DIFFERENT VOLTAGES.

3464