how to calculate the size of cable for 100 kva load,?can
somebody tell me with a formula
Answers were Sorted based on User's Feedback
Answer / naresh kumar dhal
100kva load has total current of-139 amps.
if we consider derating factor=0.8
Then total current=139/.8=173 amps
For 173 amps we can use 120 sqmm cable.
Its current capacity=1.5*120=180amps
| Is This Answer Correct ? | 34 Yes | 17 No |
Answer / piyush
what is mean of x ?& how to clculat cable sizes 35 -------
sqmm please tel in detail
| Is This Answer Correct ? | 18 Yes | 10 No |
Answer / sridhar nayak
P=1.732VI
u calculate i,take voltage 415V for three phase LT
if i=x,than cable size x=20 or 30
cable sizes are-35,75,95,120,150,185,240,300,400sqmm
it apllicable for alluminium cable only
| Is This Answer Correct ? | 16 Yes | 15 No |
Answer / kather oli
100 kva 140amps.so, 4core armoude aluminium 100 sqm 4 core
correct cable
| Is This Answer Correct ? | 13 Yes | 13 No |
Answer / manoj patel
From KVA , You get value of Amp.
By using standard cable catloge (size versis capacity)
you can find cable size.
That is only way to find cable size.From my point of
view there is no standard formula for that.
| Is This Answer Correct ? | 8 Yes | 11 No |
Answer / venkatesh
1kva=1.7amps
100kva=170amps
firstfall we are find out cable item aluminium or copper
aluminium gives 1sqmm=1amp sand copper gives 1sqmm=2amps
but we can use more than 2amps beacuse cable long time will
not come.we have to select aluminium cable for 185sqmm
beacuse total load is 170amps 185sqmm is enoff
| Is This Answer Correct ? | 14 Yes | 22 No |
how to calculate voltage drop in long distance cable? for an e.g lamp of 12 volt ac ,300watt is 90 meter away from supply i.e (x'mer 230 v / 12v)and i m getting 8 volts at lamp terminal ....
1.what is the difference between transformer differential and busbar differential.2)why we are using 2 slope for trafo diif and 1 slope for busbar diff.3)what is the purpose of metrosil and stabilizing resistor in high impedance relay circuit.4)how metrosil reduce the peak volage.5)what is the funtion of stabilizing resistor
How we can calc. the Backup time of a battery Bank???
how to choose the cable rating for load (KW)? EXAMPLE.50KW load
14 Answers ACC, NCUI, Polycab, PowerSol, Siemens, SW,
what is the contact resistance of sf6 circuit breaker??
What is meant by Low Resistance Cable and High Resistance Cable.
how to wiring 20 hp motor get completated?
How many type of ht insulator with name
1 Answers Bhushan Power Steel,
how was your last weekend.
what is the ohmic value of transformers
How do we calculate tranmission line losses of a 132 KV tranmsission line. Please give some quick tips?
What should be the conservator minimum oil level required in 2 mva transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)