how to calculate the size of cable for 100 kva load,?can
somebody tell me with a formula
Answers were Sorted based on User's Feedback
Answer / naresh kumar dhal
100kva load has total current of-139 amps.
if we consider derating factor=0.8
Then total current=139/.8=173 amps
For 173 amps we can use 120 sqmm cable.
Its current capacity=1.5*120=180amps
| Is This Answer Correct ? | 34 Yes | 17 No |
Answer / piyush
what is mean of x ?& how to clculat cable sizes 35 -------
sqmm please tel in detail
| Is This Answer Correct ? | 18 Yes | 10 No |
Answer / sridhar nayak
P=1.732VI
u calculate i,take voltage 415V for three phase LT
if i=x,than cable size x=20 or 30
cable sizes are-35,75,95,120,150,185,240,300,400sqmm
it apllicable for alluminium cable only
| Is This Answer Correct ? | 16 Yes | 15 No |
Answer / kather oli
100 kva 140amps.so, 4core armoude aluminium 100 sqm 4 core
correct cable
| Is This Answer Correct ? | 13 Yes | 13 No |
Answer / manoj patel
From KVA , You get value of Amp.
By using standard cable catloge (size versis capacity)
you can find cable size.
That is only way to find cable size.From my point of
view there is no standard formula for that.
| Is This Answer Correct ? | 8 Yes | 11 No |
Answer / venkatesh
1kva=1.7amps
100kva=170amps
firstfall we are find out cable item aluminium or copper
aluminium gives 1sqmm=1amp sand copper gives 1sqmm=2amps
but we can use more than 2amps beacuse cable long time will
not come.we have to select aluminium cable for 185sqmm
beacuse total load is 170amps 185sqmm is enoff
| Is This Answer Correct ? | 14 Yes | 22 No |
in flemings lefthand rule thumb indicate for....
Where can I get CPWD electrical shedule rates in web? please help me.
What is C-factor?why it is required to consider in fault short circuit calculations?
In TNC switch, is there any 1NO+1NC block ? and if we move over closing position, is ther any affect on trip position or vice versa?
what is the voltage and ampere rating of all range of HT conductor?
Draw SLD for a panel has 500A Bus Bar rating, with 4 outgoing, each is 80 A (load current), showing the transformer and capacitor bank rating.
Meaning of ingrace protection for motor.for ex IPXY
I am EEE student i want to improve my core side skills.how cn i approach it?
How to calculate the current rating of power cables ?
what is neutral ground resistance relay? how it is helpful in protecting system?
how much watts the computer will takes
acb(AIR CIRCUIT BREAKER)NOT CHARGING AUTO
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)