how to calculate the size of cable for 100 kva load,?can
somebody tell me with a formula
Answers were Sorted based on User's Feedback
Answer / naresh kumar dhal
100kva load has total current of-139 amps.
if we consider derating factor=0.8
Then total current=139/.8=173 amps
For 173 amps we can use 120 sqmm cable.
Its current capacity=1.5*120=180amps
| Is This Answer Correct ? | 34 Yes | 17 No |
Answer / piyush
what is mean of x ?& how to clculat cable sizes 35 -------
sqmm please tel in detail
| Is This Answer Correct ? | 18 Yes | 10 No |
Answer / sridhar nayak
P=1.732VI
u calculate i,take voltage 415V for three phase LT
if i=x,than cable size x=20 or 30
cable sizes are-35,75,95,120,150,185,240,300,400sqmm
it apllicable for alluminium cable only
| Is This Answer Correct ? | 16 Yes | 15 No |
Answer / kather oli
100 kva 140amps.so, 4core armoude aluminium 100 sqm 4 core
correct cable
| Is This Answer Correct ? | 13 Yes | 13 No |
Answer / manoj patel
From KVA , You get value of Amp.
By using standard cable catloge (size versis capacity)
you can find cable size.
That is only way to find cable size.From my point of
view there is no standard formula for that.
| Is This Answer Correct ? | 8 Yes | 11 No |
Answer / venkatesh
1kva=1.7amps
100kva=170amps
firstfall we are find out cable item aluminium or copper
aluminium gives 1sqmm=1amp sand copper gives 1sqmm=2amps
but we can use more than 2amps beacuse cable long time will
not come.we have to select aluminium cable for 185sqmm
beacuse total load is 170amps 185sqmm is enoff
| Is This Answer Correct ? | 14 Yes | 22 No |
What would be the size of wire used for 2 Ton of window A.C?
is the surge effect the solar panel, if yes so tell me how can surge effect the panel? explain brifly
what is diff btw electric,magnetic & eletromagnetic field
what will happen at the time of CT saturation?and what will be the Relay's function at the time of CT saturation?
what is REF relay?
What is AVR in Generators and How is it working.
hoW to select a CT?
name the famous power plants in ap and vwhere it is located with capacity details
why do we need to use 3c+3e cable, normally i select only 3c+e cable and i think it is enough. pls explain the usefull of 3e cable ( in this project the earthing system is well done)
1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral and body earth & panel earth.
12 Answers HP, Malladi Drugs and Pharmaceuticals, Pearl Engineering, PL,
HOW TO CALCULATE CAPACITOR BANK OR HARMONIC FILTER CALCULATION
Why synchorised generators are used for the production of electricity?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)