Answer / thakur
Simply calculate total KWH and KVH of last 24 Hrs and
Divide into-Total KWH/Total KVH=Avg PF of last 24Hrs
| Is This Answer Correct ? | 34 Yes | 9 No |
Answer / engr.abdurrahim
Dear Deepak,
Power factor is the cosine factor of the voltage & current
phase difference. Its a short defination. But if you go
deeply, Power factor=cos@,its depend only on load, instead
of phasewise.if you connect same load in every phase it
will show same power factor value in each phase.Because
power factor is depended upon load resistance=R & its
impedance=Z,
cos@ = R/Z,
So if you are going to calcualte the power factor of all
phase, you have to calculate all resistance & impedance of
the load. Then you can calulate the avg. power factor.
R=R1+R2+R3
Z+Z1+Z2+Z3
(Where Z=R+jXL=Impedance)
cos@=R/Z
Hope my answer will satisfy you.
Best Regards,
Engr.Abdurrahim
shaikh337@rediffmail.com
| Is This Answer Correct ? | 15 Yes | 7 No |
Answer / razi zainal abidin
Dear all,
This is not an answer, actually question.
In one factory, we are dificult to measure resistance,R and
impedance, Z.
What we have is only voltage supply (3phase, 420volt), and
total current flow during maximum usage using clampmeter
(including machinery, lamp, computers, etc...)
We also have info of main transformer step down because it
is in the factory area. Normally they stated value of KVA.
And some factory already install the 'capasitor bank
regulator'
So, how we can calculate the CORRECT VALUE of capasitor
need to install?
I mean, which one is the correct KW, which one is the
correct KVA, and how to calculate existing power factor IF
the factory already have 'capasitor bank regulator'....can
we switsh of the regulator?
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / reddy
By using sequence components ... (+vesequence power - -ve
seq power)/VA
| Is This Answer Correct ? | 0 Yes | 4 No |
what is meant by fuzzy logic? what is fuzzification and defuzzification?
Can a 5 core cable one end with a 32A 3p+N+E plug and the other end 32A 3p+E be used on a generator?
what is settable hystersis protection? If any body knows plz kindly post the answer..
HOW GENERATING END VOLTAGE LEVEL (6.6 KV/ 10.5 KV/ 11 KV/ 13.5 KV) DECIDED IN POWER PLANT. ON WHAT FACTORS THE GENERATING END VOLTAGE DECIDED, & WHAT IS THE CALCULATION USED FOR THIS.
I need to compare the energy consumption of an industrial machine before and after improving. Shall I compare the apparent power or the active power? I know usually factories use compensated capacitors (or other similar components) to compensate the reactive power, so if I use the apparent power, it's not the real power consumed.
where the protection CT in neutral of transformer be located, before bifurcation or after bifurcation and why.
What may be happen if neutral and earth is shorted in a substation
how will protect transformer agint overcurrent protection
What are safety features considered for Lifts during emergency?
why in India it is maintained for exactly 50HZ frequency, why it is not that 49Hz,why it is so?
can i able to get bhel previous exam question paper?
why transmission line 11Kv OR 33KV,66Kv not in 10kv 20kv?
43 Answers A2Z Group, Baiji Power Plant Gas, Electrical, HCL, Kirloskar, Mepco, NEPC, OAMC, UNI, University of Lahore,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)