how we can calculate which capacity capacitor bank we have
to add for improve pf?
Answers were Sorted based on User's Feedback
Answer / abdulsubur
p total connect load in kw =932
cos 1 =power factor before improvement =0.8 assume
cos 2= poer factor after improvement =0.9
kvar 1= ptan1 932*0.75=699.03kvar
kvar 2=ptan2 932*.4843=451.39kvar
req rating of capacitor bank =kvar1-kvar2
=699.03-451.39
=247.64kvar =250kvar
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / z_hosen
More simply,
Let total power is 1500kw
assume
cos 1 =power factor before improvement =0.75
cos 2= poer factor after improvement =0.98
tan1=0.88
tan2=0.2
and
kvar 1= power*tan1=1500*0.88=1320kvar
kvar 2=power*tan2=1500*0.2=300kvar
now, required rating of capacitor bank =kvar1-kvar2
=1320-300
=1020kvar =1000kvar
thanking u
z_hosen@yahoo.com
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / karuppiah
Let total power is 1500kw
assume
cos Q1 =power factor before improvement =0.75
cos Q2= poer factor after improvement =0.98
tan1=0.88{cos Q1=0.75,Cos-0.75=46.01degree,Now angle is
46.01,so tan(46.01)=0.88}
tan2=0.2
and
kvar 1= power*tan1=1500*0.88=1320kvar
kvar 2=power*tan2=1500*0.2=300kvar
now, required rating of capacitor bank =kvar1-kvar2
=1320-300
=1020kvar
Capacitor Bank should connect parallel with the load.
Thanks
Karups
| Is This Answer Correct ? | 2 Yes | 1 No |
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
1 Kva = How many HP
what is relation of rpm with Power supply? rpm directly Proposational to power ?
explain the f=np/120 this equ.how to come 120
3 Answers Jayaswal Neco Industries,
If a air condition consume 2.50 to 3.00 amp then how much it will consume in watts if it is running 10 hours out of 24 hours????
Determine a suitable number of slors and conductors per slot for the starter 1 winding of a 3 phase, 3300 V. SO Hz 300 rpm alternator. The diameter is 2.3 m
can some one clearly explain why -48 volt DC use in telecom site????
What will be happend if we not ground CT secondary?
3 Answers Enercon, Engro, THDC,
I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A
I need tnpsc AE Electrical question papers
2 Answers TNPSC Tamil Nadu Public Service Commission,
HOW DO A DISTANCE RELAY SENSES THE FAULTY ZONE.
WHATS THE NEED OF CT INPUTFOR AN VAPM TYPE METERING PT FUSE FAILURE RELAY
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)