Answer / abdulsubur
p total connect load in kw =932
cos 1 =power factor before improvement =0.8 assume
cos 2= poer factor after improvement =0.9
kvar 1= ptan1 932*0.75=699.03kvar
kvar 2=ptan2 932*.4843=451.39kvar
req rating of capacitor bank =kvar1-kvar2
=699.03-451.39
=247.64kvar =250kvar
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / z_hosen
More simply,
Let total power is 1500kw
assume
cos 1 =power factor before improvement =0.75
cos 2= poer factor after improvement =0.98
tan1=0.88
tan2=0.2
and
kvar 1= power*tan1=1500*0.88=1320kvar
kvar 2=power*tan2=1500*0.2=300kvar
now, required rating of capacitor bank =kvar1-kvar2
=1320-300
=1020kvar =1000kvar
thanking u
z_hosen@yahoo.com
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / karuppiah
Let total power is 1500kw
assume
cos Q1 =power factor before improvement =0.75
cos Q2= poer factor after improvement =0.98
tan1=0.88{cos Q1=0.75,Cos-0.75=46.01degree,Now angle is
46.01,so tan(46.01)=0.88}
tan2=0.2
and
kvar 1= power*tan1=1500*0.88=1320kvar
kvar 2=power*tan2=1500*0.2=300kvar
now, required rating of capacitor bank =kvar1-kvar2
=1320-300
=1020kvar
Capacitor Bank should connect parallel with the load.
Thanks
Karups
| Is This Answer Correct ? | 2 Yes | 1 No |
What is the megger value for ht
what will happen if frequency is below 50 hz?
what is motor?
Can you please explain creepage distance in detail, for a 6.6kV cable head what must the distance be and how do you determine it?
what is the chemical reaction of solt and charcoal in earthing?
how can i reduce sparking without stepdowning the voltage
How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)to improve the power factor from 0.8 to 0.9?
why constant voltage transformer should be start without load? and if started then what will happen?
What is the difference between Ac curent & DC current
what is the practical definition for voltage
when the flux enters into saturation mode then what will be the secondary voltage of the normal t/f?....high or low ? explain ...how?
what is the effect of power factor to (a) voltage (b) transformers (c) generators (d)transmission lines
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)