Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


In a 11kv/433v transformer,at the LT side ie 433 V side why
do we need to put 3.5 core Cable upto Panel.The full load
rated Amps is 666 at LV side.What value of current will flow
through the Nuetral Conductor.Why can't we use 4Core Cable
instea of that?

Answers were Sorted based on User's Feedback



In a 11kv/433v transformer,at the LT side ie 433 V side why do we need to put 3.5 core Cable upto P..

Answer / hanmanth reddy y

In a three phase system with star connected secondary
(433V side) if two phases are fully loaded to 666A and the
third phase not at all loaded the current through nuetral
conductor will be 666A. But in practice in a three phase
system that the third phase not having any load and other
two phases fully loaded is not in practice. If all the
three phases loaded equally no current flows through
nuetral and nuetral cable is not required.

Based on the requirment of transformer insulation nuetral
earthing has to be done at the transformer terminal only.

Nuetral is neccessary for single phase loads. If the
nuetral is dispensed entirely it is not possible to supply
power to single phase loads. Normally even in worst case as
huelistic judgement the nutral current will not exceed 50%
of phase current under unbalaced load conditions. Hence it
is appropriate to select cable of 3.5 core rather that of a
4 core cable.

Is This Answer Correct ?    5 Yes 0 No

In a 11kv/433v transformer,at the LT side ie 433 V side why do we need to put 3.5 core Cable upto P..

Answer / s.banik

we are always try to be distribute our load as balance
condition(i think transformer secondary side is star
connected),but in practical this not possible at
site.So,little current is flows through the neutral
conductor but this is not so high.some time we are use in
4core, this is depend on load condition & practical operation.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

why grid frequency varry time to time?

2 Answers  


If one 10 Hp 3phase induction motor connected in 380volt 50Hz. and again its connected to 380volt 60Hz. howmuch currrent and power take on both time?????

1 Answers  


Define end float in a motor?

0 Answers  


what is the long transmission lines

2 Answers  


What is difference b/w Microwave and OPGW ??

1 Answers  


what is laser diodes?

0 Answers  


how to give earthing in plain?

0 Answers  


How to design inductive load for 3 phase 440v and maximum 5 amps for star or delta? Can we use a 15kW, 1450rpm motor for 15kW, 960rpm apllication?If yes.how......n.if thesame motor used what`s it`s sideeefect.

0 Answers  


define the power factor in one word

12 Answers  


why we cannot protect 100% winding of an alternator by using differential protection?

0 Answers  


What is stray current in DC Traction?

2 Answers   L&T,


Write the force balance equation of m ideal mass element.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)