why CT output is always raetd 5.regardsof primery curre.
Answers were Sorted based on User's Feedback
Answer / balu
There are two CT output current. 5A or 1A. These are
standard outputs.There many measuring and protective
instruments will be connected to this secondary. So these
instruments designed for the output of this current. Based
on the customer primary current, the multiple factor can be
programmed to measure primary current. So, it reduces
customization .
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / ashish gupta
It consider to be standard. But if we see the ratio error and phase angle error formula we observe that turns ratio ns comes out to be in denominator.So higher the turns ratio lower is the error. So higher turns ratio is obtained when secondry current is 1 amp
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mukhesh
bec from t/f see relese the cts primary curent and
transfoemer ratio will give the exact 5a if any fault o
tr line the ratio willt if open will burnt ou be other
than 5 a ansd seec should not open at any time
| Is This Answer Correct ? | 3 Yes | 5 No |
line vltage of three phase distribution transformer is 433v and phase voltage is 250v,but we required 230v for domestic distribution,then how we reduce phase voltage of transformer
Give the selection criteria of a 3 Phase transformer for industrial purposes ?
What is the function of a capaitor in 1-phase IM?
how to calculate energy of 3-phase motor?
two TG running in parallel at equal load.one TG CB tripped in reverse power relay.after tripping found its excitation was on & turbine running at rated speed.Please clearify why that TG tripped in reverse power ?
why transformer not used to starter
Good day everyone,currently in our premise we using 30kw slip ring motor with resistance bank which we use as forward and reverse at conveyor bar handling. So,my question is how do we calculate the resistance bank which is suit the motor. Kindly,assist me... thank you
why we r used DC megger insted of AC megger?
How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f used in Canada is to be operated on 50 hz in Europe frequency then how will its KVA rating change? a-increase b-decrease c-remains same
What is the importance of RESONANCE
my project load is 6 MW so please suggest the size of cable.. ALU 3c 400 aqmm cable can be sufficient.. is there any thumb rule for calculation of cable size please help me
How Size of Busbar is determined for a particular load.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)