if 2500 KVA TRANSFORMER CAPACITY.33KV INCOMING HOW ARE
AMPEAR PRIMERY SAID
Answers were Sorted based on User's Feedback
Formula is KVA/ 1.732* volt
2500*1000/1.732*33*1000
2500/1.732*33
43.73A
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / prem
in this question is wrong because whether transformer is
delta to star or star to delta
step1 if transfomer is delta to star fourmela is
kv/volt answer is 75.75amps
step2 if star to delta fourmela is kv/volt*1.732
answer is 43.73amps
Is This Answer Correct ? | 3 Yes | 0 No |
How can I calculate the trnaformer effciency at different loading condition?
How much width of the land shall have to be left below the EHT line of 440 kv as per the rule. i am told that a corridor of 35 M width is to be left free below 220 kv line. please confirm
What is the direction of current flow in ct secondary...means if the current is flowing from P1 to P2 then what will be the direction of current flow in ct secondaryw
140 is load amps for a equipments and what ratio of CT requied for installimg ammeter to amps montering purpose?
how the BDV of the oil will be checked using moterised controled HV SET?
Advantages of using bundled conductors ?
what is function of reactor coil in Power factor correction panel
Why the isolation treasforfer are connected at out put of the ups ig 200kva ??????????????????
Electronic circuit
What is the meaning of HT Trivector Meter ?
We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Suppose we have long 2 core DC cables running from our DCDB in control room to the load (length of around 2 to 3 km). Do we need to protect these long DC cables from earth leakages or not? If yes how?
ct connection of energy meter