What is the effect of leading power factor for power
transformer & D.G?
Answers were Sorted based on User's Feedback
Answer / rabi
The stability of a generator depends on the field strength
of the magnetic field establishing in the air gap by the
rotor ampere turn. if the field is weakened the stability
margin is reduced.
Leading power factor causes field mmf (fm) to reduce and
rotor angle to increase towards 90 degree, the theoretical
operation of stable generation operation. Therefore a
machine operates well within its stability limit factor
with lagging power factor.
Transformer operation does not depend on power factor. For
that reason it is rated in KVA.
| Is This Answer Correct ? | 25 Yes | 6 No |
Leading power factor makes the current leading the voltage
it does not affect the transofmer but it affects the
D.G./Power generation unit. As for the power generation we
need to excite the excitor field which take the sensing
reference voltage from the output line of the generator.In
case of leading power factor the voltage will not dip on
increasing the load and hence the AVR will not be able to
excite the system properly.
| Is This Answer Correct ? | 20 Yes | 4 No |
Answer / deepak chander
The transformer opration does not depends on the pf. The
major problem in leading pf is related to generation.
Stator end region heating depends on the pf. In leading pf
the altenator run at underexited operation and there is the
scope for flux to increase even over the saturation limit
of core. That causes the core heating on end region.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ramesh kumar gupta
Leading power factor does affect the power Xmer within its
VA rating but it affects the D.G./a Generator unit.Due to
leading power factor the source excitation system runs in
under excited state and the deficit in excitation has to be
supplied by stator.Owing to this stator end core heating
problem observed.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / suresh
Leading power factor, means making Cos factor nearer to 1,
hence doing so you can achive the following,
1.partial reduction in load current hence losess get reduced
2.Efficency increases
| Is This Answer Correct ? | 5 Yes | 13 No |
Answer / guest
Leading power factor causes the the current to reduce,due to
which the generator gets overloaded at its full load capacity.
| Is This Answer Correct ? | 5 Yes | 34 No |
Disadventage of cable-gland earthing if any ?
cost of operation of which plant is least?
What are the tests carried out on transformer while testing at sites?..Pls explain me in detail
how mass curve differs from hydrograph.
Why we use a shunt capacitor or synchronizing Motor To Improve a Power factor pls reply me in this mail dinesh_elect_eng@yahoo.com
BRIEFLY EXPLAIN THE STORAGE CLASSES AND THEIR TYPES IN C
What is slip in induction motor?
Why we need to carry out knee point voltage test of current transformer ?
I NEED RRB SYLABUS FOR JE ELECTRICAL ,PLEASE SEND TO MY E- MAIL ID joo28_eee@yahoo.co.in
Do you have any P.L.C in your organization?
We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).
What do you mean by phasors?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)