What is the effect of leading power factor for power transformer & D.G?..

Answer / rabi

The stability of a generator depends on the field strength
of the magnetic field establishing in the air gap by the
rotor ampere turn. if the field is weakened the stability
margin is reduced.
Leading power factor causes field mmf (fm) to reduce and
rotor angle to increase towards 90 degree, the theoretical
operation of stable generation operation. Therefore a
machine operates well within its stability limit factor
with lagging power factor.
Transformer operation does not depend on power factor. For
that reason it is rated in KVA.

Is This Answer Correct ?    25 Yes 6 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / om prakash

Leading power factor makes the current leading the voltage
it does not affect the transofmer but it affects the
D.G./Power generation unit. As for the power generation we
need to excite the excitor field which take the sensing
reference voltage from the output line of the generator.In
case of leading power factor the voltage will not dip on
increasing the load and hence the AVR will not be able to
excite the system properly.

Is This Answer Correct ?    20 Yes 4 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / deepak chander

The transformer opration does not depends on the pf. The
major problem in leading pf is related to generation.
Stator end region heating depends on the pf. In leading pf
the altenator run at underexited operation and there is the
scope for flux to increase even over the saturation limit
of core. That causes the core heating on end region.

Is This Answer Correct ?    2 Yes 2 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / ramesh kumar gupta

Leading power factor does affect the power Xmer within its
VA rating but it affects the D.G./a Generator unit.Due to
leading power factor the source excitation system runs in
under excited state and the deficit in excitation has to be
supplied by stator.Owing to this stator end core heating
problem observed.

Is This Answer Correct ?    1 Yes 3 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / suresh

Leading power factor, means making Cos factor nearer to 1,
hence doing so you can achive the following,
1.partial reduction in load current hence losess get reduced
2.Efficency increases

Is This Answer Correct ?    5 Yes 13 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / shaan

SHAAN FROM MADURAI:

LEADING POWER FACTOR IN TRANSFORMER THERE ARE REDUCE
INDUCTIVE LOADS

Is This Answer Correct ?    3 Yes 11 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / guest

Leading power factor causes the the current to reduce,due to
which the generator gets overloaded at its full load capacity.

Is This Answer Correct ?    5 Yes 34 No

Post New Answer

More Electrical Engineering Interview Questions

1. If we apply dc supply to the primary winding of transformer it will be burnt out. similarly dc supply is given to field winding of syn. motor and armature winding of dc motor, they are safe. (Remember both windings inductive nature) what is the reason behind that?

2 Answers  


Two alternators say 1 & 2 are poised to parallel operation. But at the time of paralleing alternator 2 gets out of the system by tripping Earth fault relay. Please send me reply why this is happening?

2 Answers  


hi friends i m from electrical branch and seeking for tech. + apti. both papers of hpcl plz get it available as soon as possible

0 Answers   Engineers India, Engineers India Limited,


How induction stove works?

1 Answers  


what happens in a genarator when rotor supplied with ac instead of dc

3 Answers  






What are the difference between CT/PT operated Meter and RRAMR Meter for HT/LT application?

0 Answers   ABC, ACB,


How phase to phase voltage comes 440V.

0 Answers  


why it is unable to birds to be on a 220kV 0r 132 kv lines like on 33kV and 11kV lines?

4 Answers   MSETCL Maharashtra State Electricity Transmission Co Ltd,


for 644KW load which MCCB should i use

6 Answers  


What are the types of excitation system?

0 Answers  


what is the difference between electrical & electronics?

4 Answers   JSW,


george phenomenon of synchronous machine

0 Answers   JU,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)