We in my plant one of the transformer showing neutral to
earth voltage is 22V how to solve it
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Disconnect earth and measure voltages between phases and
neutral on some load.If the voltages are not equal there is
a loose connection in the star point.Before doing
this ,check the earth connection at neutral bushing.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / wasim
Check resistance of earth pit/mesh connected with Start
point (Neutral of Transformer). If reisitance is more than
5 Ohms your Neutral to earth voltage will be increased
accordingly. So you have to improve the resitance of your
earthing network to less than 1 Ohm
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aditya199307@gmail.com
Such types of problem occur due to increased in value of earth pit.
So 1st you checked the all earth pit values individually by opening all the grounded connections.
As per standard the values of earthing in HT yard should be less than 5volt.
If the value is greater than 5 volt then apply the procedure to reduce the value, which is different as per type of earthing (Normal or Chemical).
If the values should be comes as per rated value your problem is short outed.
If you talking theoretical part then voltage between N & E is zero.
But practically 2 volt is permissible but i.e. also not good for the system
It will affected on electronics system.
Such types of problem occur in the hilly areas or in rocky soil.
( If the value will not coming as per standard then add n....number of earth pits in series otherwise use counterpoise method.)
Is This Answer Correct ? | 0 Yes | 0 No |
what is appearent power?
bsec exam syllabus (mis)
How to determine stage of Automatic Power factor controlling Relay(Apfcr)?
what happens if generator is running leading power facotor?
what should be the BDV value Of 11/132kv power transformer
Why we are designed only 11Kv and 6.6Kv Alternators, not 33Kv Alternators and Power Transmission side we are designed only 220kv, 120kv, 66kv, 33kv, 11kv, and 440volts, not 20kv, 50kv, 100kv.
How does an oscillator differ from an amplifier?
Can any answer me ,What will be the range of C.T coil for L&T energy meter EM301 used for 180 kva DG set
6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200 Amp. Would there be any effect on performance of ACB due to lower voltage rating?
What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?
What is the relation between frequency and motor rpm?
A 6.6 KV motor breaker is try to Drack OUT by me while the motor running. What will Happened? a, will Trip. b,Drack Out lever will not access c, will get shock d, noting will happened