We in my plant one of the transformer showing neutral to
earth voltage is 22V how to solve it
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Disconnect earth and measure voltages between phases and
neutral on some load.If the voltages are not equal there is
a loose connection in the star point.Before doing
this ,check the earth connection at neutral bushing.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / wasim
Check resistance of earth pit/mesh connected with Start
point (Neutral of Transformer). If reisitance is more than
5 Ohms your Neutral to earth voltage will be increased
accordingly. So you have to improve the resitance of your
earthing network to less than 1 Ohm
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aditya199307@gmail.com
Such types of problem occur due to increased in value of earth pit.
So 1st you checked the all earth pit values individually by opening all the grounded connections.
As per standard the values of earthing in HT yard should be less than 5volt.
If the value is greater than 5 volt then apply the procedure to reduce the value, which is different as per type of earthing (Normal or Chemical).
If the values should be comes as per rated value your problem is short outed.
If you talking theoretical part then voltage between N & E is zero.
But practically 2 volt is permissible but i.e. also not good for the system
It will affected on electronics system.
Such types of problem occur in the hilly areas or in rocky soil.
( If the value will not coming as per standard then add n....number of earth pits in series otherwise use counterpoise method.)
| Is This Answer Correct ? | 0 Yes | 0 No |
what is meant by line voltage and phase voltage in a three phase transformer?
What will happen if the voltage in my house drops from 220V to any lower voltage?
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
How to Calculate Current Rating of SDFU (Switch Disconnector Fuse unit) for Protectionof Capacitor Bank connected to Busbar of 800Amp,in LV side of 11/0.433KV, 250KVA Transformer?
what is XF 200/240 V AC for Drawout Breaker.
In our domestic single phase line if you don't have a ground connection (earthing)how will you separately use earth in a specific power supply board.
when a pure dc signal is sent through a moving iron meter, what will it read?? dc or rms?? when a variable dc signal is sent through a moving iron meter, what will it read?? dc or rms??
Define newton's law of viscosity.
125Kva Dg can take up how much amphere load.
What is bus-bar?
which type motor r use in the celling fan.....
Please nybody say, weather the result of Bharat Oman is declared or not? Probable date of declare???????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)