Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Hi All,

I am working as a Technical executive in a MNC company and
we have 1500KVA & 1250KVA T/F in our site, can you help me
that how many maintenance tests can be conducted and what
are the procedures included for the tests can you share
yours answers and also give any web address to get more
information on this

Answers were Sorted based on User's Feedback



Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / virendra joshi

Dear friend ,

Transformer is a heart of the electrical system & that is
the reason it required more care.

Daily :-

Check the Oil level in Conservator.
check for any leakage in transformer
Check for any abnormal sound
check for Colour of silica gel.
Check for any air in Bucholz realay , if found realease
with the air vent provided in the relay.

Yearly.

Check the Dielectrica strengh of oil , filter it & if
required replace it.

Check the earthing value of a Earthpit if required topup
with salt & water.

Check the tighness of the connection both the way Primaty
side & secondary side.

Clean the transformer yard throughly.

If required lay the granuals in the transformer yard.

By proper shut down manually check the tripping point of HT
breaker tripping set points like ( OT, WT & Bucholz Relay )

check the secondary side voltage as per desired voltage &
if any missallign found adjust with the tap changer.


please revert if any quarry exists.

Is This Answer Correct ?    3 Yes 0 No

Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / tariq

in onload u cant do any test except temprature and sudden
pressur or oil level in conservator.oil leakage,cileco gel
colore for moisture,but in offload u can some more test
also.if u send ur question in detail may b i can help u

Is This Answer Correct ?    3 Yes 1 No

Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / shivakumar.s

Which type of T/F ? Tell me first.

Is This Answer Correct ?    3 Yes 2 No

Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / thyagarajan

checking of oil level in seal
reconditioning of silica gel
cleaning the bushing
check temp alarm
meger
check oil level in oltc, conservator

Is This Answer Correct ?    1 Yes 0 No

Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / dr reddy's corporate offi

hai
1)take first permission from client & hod
2)switched off the brekers
3)rack out brekers applied loto kit
4)chek primary winding bushes & secondry winding bushes
5)chek silcazel colour(breather)
6)chek oil level & density of oil(resistance)
7)primary winding , secondary winding & core bolts retigtend
8)warnish apply winding
9)take break down votage test
10)chek oil teperature & winding temperaure guages functiong
11)chek oltc counter daily basis
12)trail tests taken buchloz realy

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Why we transmit the power at the voltage in the multiple of 11 or 1.1 like 11kv, 22kv, 66kv, 132kv...... some one told me that it is due to fomr factor 1.1 of sine wave. its fine but while transforming we can choose any voltage, so why only multiple of 1.1 there also.......? plz tell me.

7 Answers  


how gen. load increase or decrease ? what happen with gen on that time

2 Answers  


how to connect from a line-to-line connection to a line-to- neutral connection?

6 Answers  


What is high frequency grounding????Applications........

1 Answers   Emerson,


sir plz send some previous year questions of jspl.

0 Answers  


What is load curve?

2 Answers  


1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.

0 Answers  


What are the safety equipments you should use while you are in a hvac switch yard

1 Answers   GPSC Gujarat Public Service Commission,


why some harmonics are disturbing while the others not

1 Answers  


Is necessary Protection CT, CLASS - 5P10 fitted at Incomer side of main Breaker ? Why ?

1 Answers  


what is load cell

3 Answers   TATA, Wipro,


WHY IN THREE PHASE CABLE 440V CURRENT FLOWS IF IN ONE PHASE 230V CURRENT FLOWS ???

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)