I am working as a Technical executive in a MNC company and
we have 1500KVA & 1250KVA T/F in our site, can you help me
that how many maintenance tests can be conducted and what
are the procedures included for the tests can you share
yours answers and also give any web address to get more
information on this
Answers were Sorted based on User's Feedback
Dear friend ,
Transformer is a heart of the electrical system & that is
the reason it required more care.
Daily :-
Check the Oil level in Conservator.
check for any leakage in transformer
Check for any abnormal sound
check for Colour of silica gel.
Check for any air in Bucholz realay , if found realease
with the air vent provided in the relay.
Yearly.
Check the Dielectrica strengh of oil , filter it & if
required replace it.
Check the earthing value of a Earthpit if required topup
with salt & water.
Check the tighness of the connection both the way Primaty
side & secondary side.
Clean the transformer yard throughly.
If required lay the granuals in the transformer yard.
By proper shut down manually check the tripping point of HT
breaker tripping set points like ( OT, WT & Bucholz Relay )
check the secondary side voltage as per desired voltage &
if any missallign found adjust with the tap changer.
please revert if any quarry exists.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tariq
in onload u cant do any test except temprature and sudden
pressur or oil level in conservator.oil leakage,cileco gel
colore for moisture,but in offload u can some more test
also.if u send ur question in detail may b i can help u
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / thyagarajan
checking of oil level in seal
reconditioning of silica gel
cleaning the bushing
check temp alarm
meger
check oil level in oltc, conservator
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dr reddy's corporate offi
hai
1)take first permission from client & hod
2)switched off the brekers
3)rack out brekers applied loto kit
4)chek primary winding bushes & secondry winding bushes
5)chek silcazel colour(breather)
6)chek oil level & density of oil(resistance)
7)primary winding , secondary winding & core bolts retigtend
8)warnish apply winding
9)take break down votage test
10)chek oil teperature & winding temperaure guages functiong
11)chek oltc counter daily basis
12)trail tests taken buchloz realy
Is This Answer Correct ? | 0 Yes | 0 No |
Generally the incandescent lamps in bathrooms fuse due to high voltage at night.What is the simple solution of this problem?
what is meant by CT`s saturation ? Can we use Metering CT`s with Protetection CT`s ?
ynchronous M/C with under excitation with reactive power absorption , acts as a) synch. Motor b) synch gen c) synchr capacit
what is the difference between UPS & Inverter
what is subtransient , transient and study state ac components
in flemings lefthand rule thumb indicate for....
Show formula which gives full load current 4.8 amps of a 3 HP motor and 27 amps of a 20 HP motor having 3 phase 460 volts, 0.8 Pf.
What is the si unit
Dear sir, By which formula u can calculate for a particular kv line there is a range of mw.
In a synchronous motor armature current flows due to revolving flux which in turn rotates the load,but in no load condition armature current is zero hence thr is no revolving flux then how motor rotates?
What are the advantages of instrument transformer?
the relationship between phase and line voltages in a 3 phase generator is expressed in what formula?