HAI,HOW TO SET THERMAL OVERLOAD RELAY FOR DOL STATRTER
FEEDER AT START AND RUNNING?
Answers were Sorted based on User's Feedback
Answer / fairos
First, for thermal overload relay has no meaning in term of setting it while on running or starting. It purely based on rated current of the motor.
when you look at the nameplate of the motor there should be a data that mention "duty" which normally either 1, 1.1 or 1.2 in value. If the duty is 1 then you can only set the overload relay at 100% of the rated current. If duty is 1.1 then the motor is allowed to operated at 10% higher than it rated current hence you can set your relay at 110% of rated.
Generally people would set at 10-15% higher than rated current. But sometimes being conservative is okay, which you can set the relay below the rated current. This can be done as long as it is not tripping unnecessarily.
| Is This Answer Correct ? | 22 Yes | 3 No |
Answer / vilas
First take a current of each phase with tong tester,while
running on normal load,
Then set the over load accordding to the load slightly
higer than normal running current, care should be taken
that it should not be more than rated current which is
always mentioned on the motor name-plate.
| Is This Answer Correct ? | 7 Yes | 7 No |
Answer / pankaj sharma
Set the relay to motor full load current as mention on motor plate
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / mohit
set thermal overal relay to 95% of full load current of
motor.
| Is This Answer Correct ? | 6 Yes | 20 No |
According to conduit size which size wiring & how many wires can we provide wires in conduit & how can we select conduit size accordingly?
wat s the difference between diode and capacitor
what is T P N bus bar
Post possible questions for Power Factor Panel FAT / SAT
i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?
what is busbar. how many types of starter.what appartus will be used to improve voltage.what is the function of starter.what is b.h.p.what material is used for earthing.
is KVAR (not reverse power) relay necessary to protect from excitor field failure on a brushless, synchroneus generator? Some people with previos experince tell me no but the manufacturers tell me it is designed for that purpose. Is it that it is only necessary for brushless generators and not the older style with the slip rings and brushes?
Describe the control mechanism of missile launcher???
only some transformers and some generator requires NGR why?
What is the bundle conductor?
What is the function of NGR for the parallel operation of alternator? whats happen when different rating of alternator are running with parallel?
What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)