HAI,HOW TO SET THERMAL OVERLOAD RELAY FOR DOL STATRTER
FEEDER AT START AND RUNNING?
Answer Posted / vilas
First take a current of each phase with tong tester,while
running on normal load,
Then set the over load accordding to the load slightly
higer than normal running current, care should be taken
that it should not be more than rated current which is
always mentioned on the motor name-plate.
| Is This Answer Correct ? | 7 Yes | 7 No |
Post New Answer View All Answers
What will happen if i replace a inductive proximity switch with photo sensor in a machine?
What is the application of Dyn1 and Dyn11 vector group of transformer?
what is the standard values(Megger test) of resistances between L&N,L&E and N&E for a system on IEE regulations?
how to get electrical supervisour certificate in gujarat
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
what is p.s impedance measurement test in earthing transformer?
Why let through energy not considered for ACB breaker while cable sizing?
Explain Continuous and Discrete signals?
write a c++ code that receives an integer number and display the sum of the number and its revers integer?
I am applying for NTPC examination.Can we please provide previous paper to my mail prasad.chintala108340@gmail.com
What is the exact formula for one weber of magnetic flux?
how to calculate energy of 3-phase motor?
how to decide choke rating for drive?
L.A. (Lightening Arrester) is located at a place from where transmission line enters the transmitting substation. So L.A. (Lightening Arrester) is the first equipments which has to encounter with lightening, high voltage surges and switching surges. It has to absorb energy of lightening, high voltage surges, and switching surges. L.A. (Lightening Arrester) is made up of layers of semiconductors. If these layers can not tolerate energy released by lightening, high voltage surges, and switching surges the L.A. (Lightening Arrester) blasts.
what will happen if frequency is below 50 hz?