how to calculate the multiplication factor in HT incomer
trivector meters
Answers were Sorted based on User's Feedback
Answer / sunil kumar das
MF=PT Ratio x CT Ratio
Ex: PT ratio= 33KV/110V
CT ratio= 40/1A
so please this value in formula
MF: 33KV/110V x 40/1A = 12000
| Is This Answer Correct ? | 119 Yes | 46 No |
To calculate MF(multiplication factor) we must know current
transformer ratio and meter ct ratio
mf = current transformer ratio/meter ct ratio
| Is This Answer Correct ? | 75 Yes | 34 No |
Answer / mohamed ali.m
Hi,
this Correct Ans,
MC = PT Ratio x CT Ratio x Dial Constant/ Meter PT Ratio x
CT Ratio
For Exmple : 100x60x1/1x1 = 6000( This MF)
| Is This Answer Correct ? | 30 Yes | 20 No |
Answer / ripun
Mf=field ct ratio/meter ct ratio *field pt ratio/meter pt ratio
Let field ct ratio=15/5a
Field pt ratio=11kv/110v
Meter ct ratio=-/5a
Meter pt ratio=-/110v
M.F=15/5*1100/110=300
| Is This Answer Correct ? | 21 Yes | 15 No |
Answer / chandu
multiplication factor is depending upon CT Ratio Thats o.k
but if meter constant is given what will be the
multiplication factor for 600/5 CT
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / er l r daroch
Line ctr 50/1a
Meter ctr 50/5a
Is it a right combination
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / sureshmuthusamy
MF = External ct ratio*external pt ratio/metering ct ratio* metering pt ratio(if there)
= 40* (110000/110)/1*1
= 40*1000
=40000kw
= 40w(40000/1000)
so,MF is 40(your daily tariff meter consumption (kwh)*40= consumption /day.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / rajesh sutar
MF= CONNECTED CT/METER CT *CONNECTED PT RATIO/METER PT ratio
*space factor
(space factor =1)
| Is This Answer Correct ? | 5 Yes | 12 No |
how the alternator transfere mechanical energy to electrical one ??
What core magnetic balance test of transformer? How to do this test in a three phase Star delta (star-LV, Delta-HV) transformer? How to measure and where to measure? thanks and regards Austin
22 Answers Neutech, Power Grid, TSSPDCL,
why we use 50 hz frequency in india .. why not 60 hz
How to control motor gearbox speed and friquency? If length of cable and dia given, how to measure the voltage drop?
how i run d.c. moter with solar panel without use of battery?
I am abt to give IOCL intrv.Plz sir guide me for IOCL intrvw (Electrical).Which subject to be consider. questions are generally asked from which subject.Plz help me out.
can we use HT cables for LT power supply ?
1. alternator has full load regulation of 4% when pf of the load is 0.8 lag, 1500 rpm. full load regulation of 1400 rpm for 0.8lag will be ________ ?? 2. torque angle of a sync m/c operating from a constt voltage bus is usually defined as space angle between _______ . 3. method most effective in finding out no load losses in large DC shunt motoris ______ . 4. current carrying capacity of fuse material depends on ______ . 5. coil has res. 10 ohm, inductance 1H. what wil be current after 0.1sec after switching on to a 500V DC SUPPL ? ? 6. effect of phase lag compensation on servo systems ___________ . 7. rotor of a dc machine is usually supported upon ______ . 8. DC motor is preferred to AC motor in which application ?? 9. 3 nos of 10:1 Xmer are connected in Star-Delta to supply a load at 230V.the supply voltage must be ______ . 10. voltage source produces max current in which circuit. 11. cal. power, if current and voltage are out of phase by 90 degree. 12. suitable length of Xmission line of power at 66 KV. 13. Which of the theorm helps in simple computation when the load across a ckt is varying ?? 14. what is the adopted line length for power Xmission of power by cables ??
What are the different methods of improving power factor,especially in Wind Sector
what is the difference in inductance and resistance.both oppose the flow of current but how.resistance having + ve power in both cycle while inductance having both power.
how is the incoming cable size calculated for a given current rating of a panel??
how we control automatic generator i'e with to supply (main supply and local generator) when the main supply was break to supply the local supply automatically to begin supplying power.I now this control circuit is the combination of contactor time delay contactor switch and overload relay .but my question is how we combine those component thank you
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)