how to calculate the multiplication factor in HT incomer
trivector meters
Answers were Sorted based on User's Feedback
Answer / sunil kumar das
MF=PT Ratio x CT Ratio
Ex: PT ratio= 33KV/110V
CT ratio= 40/1A
so please this value in formula
MF: 33KV/110V x 40/1A = 12000
| Is This Answer Correct ? | 119 Yes | 46 No |
To calculate MF(multiplication factor) we must know current
transformer ratio and meter ct ratio
mf = current transformer ratio/meter ct ratio
| Is This Answer Correct ? | 75 Yes | 34 No |
Answer / mohamed ali.m
Hi,
this Correct Ans,
MC = PT Ratio x CT Ratio x Dial Constant/ Meter PT Ratio x
CT Ratio
For Exmple : 100x60x1/1x1 = 6000( This MF)
| Is This Answer Correct ? | 30 Yes | 20 No |
Answer / ripun
Mf=field ct ratio/meter ct ratio *field pt ratio/meter pt ratio
Let field ct ratio=15/5a
Field pt ratio=11kv/110v
Meter ct ratio=-/5a
Meter pt ratio=-/110v
M.F=15/5*1100/110=300
| Is This Answer Correct ? | 21 Yes | 15 No |
Answer / chandu
multiplication factor is depending upon CT Ratio Thats o.k
but if meter constant is given what will be the
multiplication factor for 600/5 CT
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / er l r daroch
Line ctr 50/1a
Meter ctr 50/5a
Is it a right combination
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / sureshmuthusamy
MF = External ct ratio*external pt ratio/metering ct ratio* metering pt ratio(if there)
= 40* (110000/110)/1*1
= 40*1000
=40000kw
= 40w(40000/1000)
so,MF is 40(your daily tariff meter consumption (kwh)*40= consumption /day.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / rajesh sutar
MF= CONNECTED CT/METER CT *CONNECTED PT RATIO/METER PT ratio
*space factor
(space factor =1)
| Is This Answer Correct ? | 5 Yes | 12 No |
What is chopper
what is a kit kat fuse?
X/R ratio in 11kv transmission line is?
can anybody give me current carrying capacity of cables e.g size of cable in sq.mm & its current capacity both alluminum & for copper
Does Lightening arrest requires Earthing?..
whats the existence of reactive power and when it arises?
what is the unit of current
What is PIR (pre inserting resistance) in 400kv EHV SF6 BREAKER? Why it use?
Can we use delta-star neutral grounded 3 phase power transformer bi-directionally.
why shoud in High tension cable( above11KV etc.,)a semiconducting material coating will be there on insulation?
how am i achived model paper to prepratio for bhel exam
what are the values to be accepted on 3 core 185sq mm for 11000volts on insulation resistance between conductors and between conductors and earthed?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)