how to calculate the multiplication factor in HT incomer
trivector meters
Answers were Sorted based on User's Feedback
Answer / sunil kumar das
MF=PT Ratio x CT Ratio
Ex: PT ratio= 33KV/110V
CT ratio= 40/1A
so please this value in formula
MF: 33KV/110V x 40/1A = 12000
| Is This Answer Correct ? | 119 Yes | 46 No |
To calculate MF(multiplication factor) we must know current
transformer ratio and meter ct ratio
mf = current transformer ratio/meter ct ratio
| Is This Answer Correct ? | 75 Yes | 34 No |
Answer / mohamed ali.m
Hi,
this Correct Ans,
MC = PT Ratio x CT Ratio x Dial Constant/ Meter PT Ratio x
CT Ratio
For Exmple : 100x60x1/1x1 = 6000( This MF)
| Is This Answer Correct ? | 30 Yes | 20 No |
Answer / ripun
Mf=field ct ratio/meter ct ratio *field pt ratio/meter pt ratio
Let field ct ratio=15/5a
Field pt ratio=11kv/110v
Meter ct ratio=-/5a
Meter pt ratio=-/110v
M.F=15/5*1100/110=300
| Is This Answer Correct ? | 21 Yes | 15 No |
Answer / chandu
multiplication factor is depending upon CT Ratio Thats o.k
but if meter constant is given what will be the
multiplication factor for 600/5 CT
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / er l r daroch
Line ctr 50/1a
Meter ctr 50/5a
Is it a right combination
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / sureshmuthusamy
MF = External ct ratio*external pt ratio/metering ct ratio* metering pt ratio(if there)
= 40* (110000/110)/1*1
= 40*1000
=40000kw
= 40w(40000/1000)
so,MF is 40(your daily tariff meter consumption (kwh)*40= consumption /day.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / rajesh sutar
MF= CONNECTED CT/METER CT *CONNECTED PT RATIO/METER PT ratio
*space factor
(space factor =1)
| Is This Answer Correct ? | 5 Yes | 12 No |
if the back emf eqution for dc motor EB=(QPNZ/60A) THEN what is the value of A for PMDC MOTOR OR how can dicide the value of "A"
how can we judge the percentage of load on the basis of temperature differences readings between WTI and OTI in a transformer
what should be the air clearence between phase to phase, phase to earth in Medium voltage switchgear for 3.3kv,6.6kv,11kv,22kv and 33kv? Which is to be referred for this?
What will happen if the field of synchronous generator is removed when it is in operation with no load?
What is application/Function of Electro chlorinator in Offshore Oil & gas Platform ?
what is impedance in a transformer? how can i calculate it?
Define working of prim mover governer in alternator?
I have 11KV/415V power distribution transformer. I have found unbalance current in LT (415V) side. Also observed that unbalance voltage (3V) at LV side due to HV side unbalance voltage. What should I check for this? Also, the same LV side load can run in balance on captive power.
magnetic circuit consume energy
IN HT MOTOR HT REFERS TO HIGH TENSION OR HIGH TRANSMISSION?
what mean ohm
How to do maintenance of transformer feeder.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)