what is hormonics. how it is generated & what are the
problem faced by that.
Answers were Sorted based on User's Feedback
Answer / mihir gajjar
*Simply Harmonics is Integral multiple of fundamental
frequency.* By means of different euipment different order
harmonics are generated 3rd harmonics generated by AC
Generator itself,5th harmonic generated by transformer&
different order harmonics are generated by electronic
circuit like rectifier,inverter o/p.
*Harmonics spoils many component in power system.
problems like mal function of MCBs,Excessive Heating in
neutral conductor,excessive eddy current loss in conductor
due to skin & proximity effect,it creates the problem in
Motor & Tranformer iron loss.
| Is This Answer Correct ? | 24 Yes | 3 No |
Answer / saikishore.katuri
Harmonics is Integral multiple of fundamental
frequency.That means if the fundamental frequency is f, the
harmonics have frequencies f, 2f, 3f, 4f and the property
is that they are all periodic at the fundamental
frequency.The sum of harmonics also periodic at that
frequency.
If we see the generation of harmonics different order
harmonics are generated 3rd harmonics generated by AC
Generator itself,5th harmonic generated by transformer&
different order harmonics are generated by electronic
circuit like rectifier,inverter etc..
It creates many problems like in power systems are
Harmonics can cause all sort of problems Excessive Heating
in
neutral conductor,excessive eddy current loss in conductor
due to skin & proximity effect,it creates the problem in
Motor & Tranformer iron loss.It will give problem on
waveform distortion. To avoid this designing of the neutral
cable size very important.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / graeme
Harmonics are frequency components that are whole number
multiples of a fundamental frequency. For example, in a
60Hz AC supply system, 2nd harmonic is 120Hz, 3rd harmonic
is 180Hz and 4th is 240Hz.
Harmonics are most often caused by non-linear loads (eg
transformers where the line current is distorted by the non-
linear B-H characteristics in the core), rectifier circuits
and phase control circuits. In all these cases, the
resulting load current waveform is not a pure sine wave, so
harmonics are present.
Harmonics can cause all sort of problems such a voltage
waveform distortion and the different harmonic frequency
components causing different impedance values to appear in
reactive components.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / shahul
Harmonics Generally created in Non-Linear Circuits,for
eg.VFD,Inverters..etc.
It will create problem on waveform distortion.So designing
any power system with non-linear circuits harmonics to be
considered so that designing of the neutral cable size very
important.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / kirthika
In fourier transform the complex waveform can be shown to
be built of a series of sinusiodal waves whose frequencies
are integral multiples of frequency of fundamental wave is
harmonic functions are called harmonics
| Is This Answer Correct ? | 12 Yes | 10 No |
what will happen if phases are not shorted with neutral in transformer impedance test? and if neutral is not connected with ground?
what is the function of impulse relay
what is anti-pumping relay and the significance of it in a switcgear cb control system?
Will an earth leakage trip be activated if the component or wiring is faulty on low voltage equipment.Example An electrical Cat Scarer placed in the garden and water gets into the wiring.
why do mostly prefer to generate and distribute electricity in 3 phase..not in 4 phase or 5 phase.??
will 1050kva DG set withstand for back charge of 16MVA transformer
Why does the power consumed is always constant even if a fan speed is altered?
how rating of transformer is selected for any new plant/what kind of load is cosidered/what kind of fadtors are considered/ pz give standard procedure
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
Make a list of materials and layout diagram for a 35hp motor, to be wired at 35meter away from the MDB in a chemical factory.
for preparation of design note of 11 / 220 kV , 3 phase, 63 MVA transformer how can calculate or consider the iron losses and copper losses
why the voltage is in digit of 11/33/132/220/440 please send me on shukrerabbi_abkhalil@rediffmail.com with thanks
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)