How to Calculate the maximum Demand required for a
connected load for a manufacturing Plant
Answers were Sorted based on User's Feedback
Answer / mior
First of all, you need to know your total connected load
(TCL). Then, you apply Diversity Factor at your TCL to get
the Maximum Demand (MD).
Example;
You have 1no. 36W Florescent Lighting and 1no. socket outlet
(250W). Your TCL will be (36W + 250W) = 286W.
In actual, the TCL may only contribute certain percentage
for your MD; that's why you need to apply Diversity Factor
(DF).
Common practice, light fitting will contribute 80% and
socket outlet giving 40% for your total MD.
Hence, your total MD will be = [(36W * 80%)+(250W*40%)
]= 128.8W
Therefore, your total MD to be declared for your Utility
Provider will be 128.8W.
The link below might help your for more info.
http://guide4electricalconsultant.com/calculate%
20tcl&md.html
Is This Answer Correct ? | 72 Yes | 13 No |
Answer / sachin
First try to know what is mean by max demand . Max demamd
is the simutaneous max requirment of power for any unit.
there is no standard practise to calculate the MD of any
unit . but one can carry out as follows.
1] CALCULATE THE TOTAL CONNECTED LOAD .
2] APPLY DIVERSITY FACTOR - IT IS THE PART OF EXPERIENCE
AND MAY VARY FROM UNIT TO UNIT .
3] TOTAL CONNECTED LOAD X DIVERSITY FACTOR = MAX DEMAND
Is This Answer Correct ? | 27 Yes | 9 No |
Answer / yogish
There is no specific method to calculate the MD from the
CL. It really depends on the following: -
1. Type of industry: Continuous or Batch process, Heavy or
Medium or Small
2. Mechanical load or Heating load or Furnace load
3. Plant at infant stage or stabilised
4. Standby loads included
5. Largest single load and its starting method
6. Possibility of staggering load without affecting
activities.
7. Whether the major motors are optimally sized or oversized
We can get at some figure, only by experience in a similar
industry.
Is This Answer Correct ? | 41 Yes | 25 No |
Answer / parag nikumbh
MD in KVA = (connected load in kw x Diversity factor) / P.F.
Diversity factor can be calculated as Running load/Installed load
Is This Answer Correct ? | 20 Yes | 5 No |
Answer / j manikanta
Can you clarify my doubt.
we have a Total connected load 100 KW. We want to take an HT Connection in Andhra pradesh. So how much KVA will be sufficient for my plant. Kindly suggest me about CMD.
We will use 80-90% of Connected load. And what is diversity factor. how we need to calculate this
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / kanand078
first calculate the total load in plant. and find the
voltage and current,after u can use this formula and
calculate the MD=V*I
Is This Answer Correct ? | 24 Yes | 62 No |
How to Calculate Current Rating of SDFU (Switch Disconnector Fuse unit) for Protectionof Capacitor Bank connected to Busbar of 800Amp,in LV side of 11/0.433KV, 250KVA Transformer?
A 3ph load of 10 KW is equal to how many KW of single phase .
i have to use generator in my project,which gen. i can use?
why earth hole size is biggest in plug point?
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test.
What is P.F? Formula for calculating PF in HT side?
Why the ceiling fan rotate in anticlock wise direction whereas tables fan rotates at clock wise direction?
what is the Transformer Protection & Type ??
when we conduct high voltage testing why milli amp. is required?
explain impact of tariff on energy management..? and what is ABT tariff
What current flows in the transformer primary when its secondary is open?
What Normal(Tangent) towers and Tension(Cut-point) Towers?
1 Answers ABB, BGR Energy, NTPC, Powermec,