what is the principal of star delta starter?
Answers were Sorted based on User's Feedback
Answer / sayan
The pinciple of a star dela starting is based on the fact
of reduction of the starting current at the time of
starting of the motor. But there is always a surge of
current whenever there is a transition from star to delta.
This is essentially useful for the motors which are
connected to systems which are prone to have a voltage dip
at the starting of the motor.But the only disadvantage of a
star delta starter is that the starting torque reduces
appreciably during starting the motor in star.
| Is This Answer Correct ? | 111 Yes | 13 No |
Answer / shyam prakash ray
The principal is to keep the starting current in safe limit
so that the motor achieves 70% of speed as connected to
star side, since the motor draws very high current at the
time of starting due to high starting torque.
Once the motor gets started then it is changed/converted
into delta side either manually or automatically for
running.
| Is This Answer Correct ? | 32 Yes | 7 No |
Answer / ravinder kashyap
work of a starter is reducing high starting current
in star connection voltage is Vph=Vl/root 3
so at starting time of motor we are use star connection at
starting star connection are use then after picking normal
speed after this delta connection are applied to motor
this is the principle that by use of star /delta voltage
conversion scheme
| Is This Answer Correct ? | 25 Yes | 5 No |
Answer / amit vishwakarma
Star delta starter used for squirrel cage motor,utilises the principle of reducing the starting voltage.all the six terminals( each of two) of 3 phase induction motor are brought to the starter ......
In fact start delta starter is simply a two way switch. The method is based upon the principle that with 3- winding connect in star, the voltage across each winding is 1/√3..i.e.57.7% of the line to line voltage whereas, the same winding connected in delta will have full line to line voltage across each.
The star delta starter connects three stator winding in star across the rate supply voltage at the starting instant. After the motor attain speed, the same winding through a change over switch are connected in delta across the same supply voltage..
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / guru
TO REDUCE THE STARTING CURRENT FOR SERIES MOTORS.
| Is This Answer Correct ? | 12 Yes | 8 No |
Answer / ernest parku
Star is to reduced the high starting torque of the motor or the high surge current to a full load of delta connection.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / ganesh ghule
The pinciple of a star dela starting is based on the fact
of reduction of the starting current at the time of
starting of the motor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / guna sekhar
induction motor draws 4times the load current of motor intially. so we use star -delta starter to reduce intial current . first the windings connected in star thereby reduces the intial current by 1/../3[root3].after certain time delay its converts winding connection to delta.
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / ketan
Reduction starting curernt because of current is devided in
phase 60%.
| Is This Answer Correct ? | 11 Yes | 15 No |
how capacitor can split the phase.
Power factor =1.000 at factory in supply. However, PF = 0.8 at motor end. Current = 100 Amp, Voltage = 400 V. What is the power distribution loss? Can I reduce it by adding capacitor at the load feeder?
What is the criteria that generally follow by distribution licenses to fix contact demand of their industrial customers?
What are the commercial names of overhead conductors used in India?
can we say current flows inside an atom as electron moves inside an atom?
difference b/w series¶llel
what is the main difference between power devices and signal devices
What happens when reactive power enters a system?
What is the diffrence between PL Lamps and CFL Lamps
operating Lt & HT voltages used in India?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
will three phase energy meter run without one phase
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)