When alarm is activated in buccholz relay in transformer
Answer / spl
Depending on the model, the relay has multiple methods to detect a failing transformer. On a slow accumulation of gas, due perhaps to slight overload, gas produced by decomposition of insulating oil accumulates in the top of the relay and forces the oil level down. A float switch in the relay is used to initiate an alarm signal. Depending on design, a second float may also serve to detect slow oil leaks.
If an arc forms, gas accumulation is rapid, and oil flows rapidly into the conservator. This flow of oil operates a switch attached to a vane located in the path of the moving oil. This switch normally will operate a circuit breaker to isolate the apparatus before the fault causes additional damage. Buchholz relays have a test port to allow the accumulated gas to be withdrawn for testing. Flammable gas found in the relay indicates some internal fault such as overheating or arcing, whereas air found in the relay may only indicate low oil level or a leak.
Is This Answer Correct ? | 3 Yes | 0 No |
how much cuurrent flow through human body effected ????
7 Answers Divis Laboratories, ICSA,
if d gen is 50kw,load is 60 kw,hw d gen ll supply d remaining power?
one split ac how can told of this ac which Tr tell me us
If o/p power is doubled by how much does the sound increase
How to calculate % Impedence?
What is use of reactor..how it is help ful in electrical system .....brief explain
i have been tasked with a design of protection, metering and control(PMC) relay panel extension to accommodate all PMC relays.There is an already existing panel where this one will be built.What are the design aspects for this kind of project? thank you.
Please give the formula for converting from 1 tr refrigeration to kw.
what is hysteresis loss?
what is the formulae for selcting capacitor bank to increas pf
Which capacitor is preferred for high voltage and frequency?
What is restricted earth fault protection ?