When alarm is activated in buccholz relay in transformer
Answer / spl
Depending on the model, the relay has multiple methods to detect a failing transformer. On a slow accumulation of gas, due perhaps to slight overload, gas produced by decomposition of insulating oil accumulates in the top of the relay and forces the oil level down. A float switch in the relay is used to initiate an alarm signal. Depending on design, a second float may also serve to detect slow oil leaks.
If an arc forms, gas accumulation is rapid, and oil flows rapidly into the conservator. This flow of oil operates a switch attached to a vane located in the path of the moving oil. This switch normally will operate a circuit breaker to isolate the apparatus before the fault causes additional damage. Buchholz relays have a test port to allow the accumulated gas to be withdrawn for testing. Flammable gas found in the relay indicates some internal fault such as overheating or arcing, whereas air found in the relay may only indicate low oil level or a leak.
| Is This Answer Correct ? | 3 Yes | 0 No |
What is GNR ? How much value of ground neutral resistance?
which Machine u will prefer to use at place where Flammable gases are coming out & why ??
WHICH TYPE OF TRANSFORMER USED IN SWITCHYARD IN POWER PLANT?
15 Answers GE, Lanco, NTPC,
why we use low kv lightining arrester in line for example 9 kv using in 11kv
WHAT HAPPEN WHEN CT SECONDARY OPEN DURING LOAD
HELLO SIR, IAM PREPARING HPCL EXAMS. SO PLS SEND MATERIAL OF HPCL ELECTRICAL ENG..TO VIJAY_8888@YMAIL.COM
What can a fresh(without experience) electrical engineer contribute to NTPC( Or any PSU company) growth?
Hi frnds :) plz tell me that i have 100 KVA 3 phase generator so by thumb rule 100*1.4 = 144 amps and generaly we can operate at 80% load...so it will 144*0.8 =112 amps.... so now i m confused about single phase load.....if we use that generator only for single phase the that 112 amps is total single phase load or i can give 112 amps at red 112 amps at yellow and 112 amps at blue.... i mean that total single phase load that 100 KVA generator will take is 112+112+112=336 amp ??
1.What is the range of stator resistance of 3-phase induction motor? 2.Two electrically operated vibro motors are foxed in parallel direction in vibrating feeders. what is the direction of both vibro motors?
what time should we set to come on star contacter in stardelta starter?and for what reason we hav to set such time delay range?
132/66kv sub-station procation ?
Why Generator rotate only clock wise ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)