HOW TO FIND OUT 1. LINE CURRENT, 2. PHASE CURRENT IN AN
ALTERNATOR / TRANSFORMER WHICH IS FEEDING A I)STAR LOAD ii)
DELTA LOAD, USING A CLAMP METER.
NORMALLY WHEN WE USE CLAMP METER IN A DG SET THEN WHAT DO
WE GET?? PHASE CURRENT OR LINE CURRENT.
Answers were Sorted based on User's Feedback
Answer / debasish das
we can not measure phase current in three phase suply. if
we measure the current that will be the line current .and
if we devide this current by .732 then we will get phase
current
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / rahul
u can find the phase current from the CT out going. then u
calculate the line current herewith
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / vivek
dear sudheer, the question was to find it out practically,
as i wrote, using the clamp meter ..... theory we all know
but thequestion is how to apply the knowledge .... let me
ask the question in a different way..... where exactly
would u put the clamp meter in order to measure the line
curren and phase current?? because phase current passes
through the neutral and the line current through two
phases. .... so i guess one might need to open theload or
the source especially in order to measure the phase
current ....if anybody knows a link from where i can get
practical knowledge like this then pl let me know....
thanks.
| Is This Answer Correct ? | 6 Yes | 11 No |
HOW TO CALCULATE THE REGULATION OF 100 AND 25 KVA TRANSFORMER
can we individually produce electriciyt
Why machines are avoided to work is saturation region of B- H curve?
If you touch power transformer........ Then , in your body current will flow or not...?
In UPS what does 600va reffer to?
11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??
Which one is given high energy in same power consumption AC or DC
if there is a voltage difference between neutral and earth when we operate any instrument for fraction of time then where is problem?
How can identify meter AC or DC without use of symbel?
why in India it is maintained for exactly 50HZ frequency, why it is not that 49Hz,why it is so?
a 50hz motor to give 60hz whats happening in motor.what happen the motor.
How CT & PT ratings are decided for a 11KV or 33KV transmission line?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)