how to check thermocouple ,its working or not?
Answers were Sorted based on User's Feedback
Answer / v.r.m.kiran
check physicall condition.
Then check the resistance of therocouple.
if it is open theremocouple is dead.
if it showing some ohms nearer to Zero. Then it is ok.
Then heat the thermocouple check the mv & verify with the
standard chart.
| Is This Answer Correct ? | 61 Yes | 7 No |
Answer / eswar
by checking the resistance/voltage between the terminals of
thermocouple we can say that it is working or not
| Is This Answer Correct ? | 50 Yes | 22 No |
Answer / sivakumar
take a digital multimeter.. put it in mV Mode and place the
leads in to the thermocouple terminals .. check the mV IS
showing 0.01 for ktype (26degree celcius)... then hold the
measuring junction of the thermocouple in ur hand ..then
observe the changes.. it will vary slightly..
Note:- thermo couple leads are case sensitve(+/-) there are
different colour codes(for ktype yellow and red wires are
used cu, al yellow= positive, red= negative..)
| Is This Answer Correct ? | 27 Yes | 0 No |
Answer / mail2noor.hyd
T/C is working/?
1 check the thermocouples physical status, it is physically ok.
2 check the leads(terminals) ok
3 measure the room temp. in mv with the help of DMM
4 t/c kept in heat compared result mv vs temp.
| Is This Answer Correct ? | 28 Yes | 4 No |
Answer / arjun
the thermocouple is connected to the multimeter,and the
multimeter is set to volt, it shows reading of 0mv.the
principle that is used in thermocouple is seeback effect.
| Is This Answer Correct ? | 32 Yes | 21 No |
Answer / vinayak
To check the thermocouple, its mv is measured at the
terminals connected. the corresponding mv is compared with
mv v/s temperature chart & the value should tally with the
process / operation parameters
| Is This Answer Correct ? | 15 Yes | 7 No |
Answer / senthilnathan.j vizhidiyur
If you are going to test k-type thermocouple at normal room
temp.first you check the resistence of the themocouple using
multimeter.if junction is open then it shows Mohms means the
thermocouple is dead.it will show 0 resistence when it is in
good condition. then you check the milllivolt output by
touching the terminals with correct polarity (For k-type
red-positive; green-negative) using multimeter.at room
temprature the output of thermocouple is 0mV because both
the hot junction and cold junction are in same temprature
say 30deC.
then set the hotbath temp. into 100C and put the T/C inthat
and now check the T/C teminals it should show 4mV because
for K-type For 1degC =0.04mV will rise.It is difficult to
find that much minimum voltage.so that only we are taken the
reading at 100degC. now you are successfully tested the
Thermocouple.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / a
CHECK CONTINUITY OF T/C LEADS AND MV O/P WHILE HAETING ITS
JUNCTION.
| Is This Answer Correct ? | 13 Yes | 8 No |
Primarily You can check the continuity of the t/c and
confirm its live or dead, measure the mV for the room
temperature it will show 0 mV. then rub the t/c end with
your hand, so that the mV will increase slightly. To check
it in higher temperatures use temp bath.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / subash konar
If the thermocouple is ok then by heating one junction there
will be emf produced at another junction which we can
measure by voltmeter
| Is This Answer Correct ? | 5 Yes | 1 No |
what is exat meaning of compentation in RTD ? what diffrent between 2 wire,2 wire and 4 wire RTDs?
how do i calibrate mmwc pressure guage with out calibrator.if any? pls give me the ans.
how eddy current loss in probe and induced gap voltage accros probe trip and shaft
in i/o panel for digital ouput(do) how much power(in volts) we must give?
what should be distance from tapping point to inallation place of instruments?
3 Answers Tasnee Petrochemicals,
what happen if i install my pressure transmitter below the elevation of pipe in natural gas service. Also support your answer
To calculate temperature, why we multiply 25 with mV?
hello i'am samad.Any one Can help me! How to calibrate Vaccum Transmitter DP Type range 0 - 50 mbar abs by hand pump calibrator.
What is Difference between Bench Set & Operating Range of Control Valve?
I want to take temp. data from recorder to computer. Which communication system is best from this option(Rs 232- 485/ethernet/USB)?
What is Trim?
WHAT IS AN INTERLOCK SYSTEM ?? HOW THEY WORKs ?? WHERE IT IS USED ??? MAINLY ??
2 Answers TATA, Tata Steel Limited,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)