how to check thermocouple ,its working or not?
Answer Posted / vinayak
To check the thermocouple, its mv is measured at the
terminals connected. the corresponding mv is compared with
mv v/s temperature chart & the value should tally with the
process / operation parameters
Is This Answer Correct ? | 15 Yes | 7 No |
Post New Answer View All Answers
I faced several time siemens ps2 positioner automatically getting Chang in it's set point direction after auto calibration So is there any causes biside this or any permissives ?
what is zero and span ?
i want to know the interview format fot gail, instrumentation. pls answer me in habib.sami1003@gmail.com
Why 4-20 amps is being used in instruments? Why cant we use any other range instead of 4-20 amps? Why only 4 amps is taken as lower limit and why 20 amps is taken as the higher limit?
How to regulate the flow of Air in 4" line, with max flow of 330 nm3/hr and Pressure of 0.5 bar? please suggest the type of instrument required.
State four different types of flow measurement, for gas flow measurement MMSCFD is the common unit expand the unit and specify significance of word S in the unit.
what is orfics working in main steam line. is it increase pressure, velocity of steam flow and dicrease steam flow rate. or any other
What is the cascade control
How does a single acting, spring return ball valve actually work? Does it require continuous air supply?
what is the procedure to callibrate temp controller ,pressure controller,etc. suppose a temp controller showing error 1.5 degree centigrate how can i minimize it.
Which is the best field foundation bus. ( FF ) Yokogawa, Honeywell or others ?
With N nodes and B branches what will have a network ???
What is the difference between uv and ir scanners? and what is the workig principle of both
If P will increase then what will happen with PID?
In Safe Guarding test what means by "Failed to Danger" ?