Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


A DP Endress and Hauser flow transmitter is always tripping
pump at low flow. set point is 74 cubic meter/hr. Thorough
impulse line flushing and zero calibration has been done,
yet problem persists. What do you think is the problem and
how do you rectify this fault?

Answers were Sorted based on User's Feedback



A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / carl ellis

The stated question assumes that the design criteria for a
low flow alarm SP at 74m^3/hr is valid. It is not clear
whether the problem is limited to the instrumentation
without a clear statement that the pump has been determined
to be operating properly. Since this is an instrumentation
exam, I'll assume the problem is in the instrumentation.

If the instrumentation is the problem, then the DP's
indicated DP/flow rate has to be lower than the alarm SP.
What can cause a DP transmitter to indicate a lower
DP/flowrate than it should?

If the equalizing valve is not tightly closed or leaks at
the valve seat, the DP will be lower than it should be as
the DP approaches zero, depending on the leak rate.

Damaged orifice plates read low, resulting in low indicated
DP readings.

Lower line pressure than the "design" line pressure will
reduce the indicated DP reading.

Someone changed out the orifice plate (OP)with an OP with
bigger bore or re-installed the correct OP backwards.

Since DP operation is "high side pressure minus low side
pressure equals indicated DP", a leak anywhere on the high
side will reduce the high side DP pressure and result in a
low indicated DP. That could be
- leak in the high side impulse line or its fittings
- manifold valve flange gasket leak on the high side or on
the process side
- vent leak
(however liquid leaks are usually visually evident)

In a mis-configured system, the PLC/DCS might have square
root extraction in addition to square root extraction on the
DP transmitter, which would cause a low flow rate indication
at the PLC/DCS.

Tell 'em Carl sent you.

Is This Answer Correct ?    7 Yes 0 No

A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / mohamed

You should see the time delay of the alarm itself and the time lag of the transmitter

Is This Answer Correct ?    3 Yes 0 No

A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / mukesh singh

increase the tripping time,your transmitter might be malfunctioning..follow the trend of DP.

Is This Answer Correct ?    1 Yes 0 No

A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / ntia

Check the strainer of your pump..remember that your pump supplies the pressure...if the pump strainer is dirty...it will be be giving low flow and since your dp was set to shutoff the pump at a low flow..then your dp will continue to shut off the pump until the pump is cleaned and the fault is rectified.

Is This Answer Correct ?    0 Yes 0 No

A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / samir

If it is a malfunction of flow transmitter then you should cross check with portable ultrasonic flow transmitter. Whether it is showing correct or not. & then you can follow previous advise.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

How to calibrate smoke Dectector

0 Answers   KOC,


diff between neutral ,ground,phase , earthing and shielding?

0 Answers   L&T,


can we replace a slot sensor (inductive type) with limit switch (potenial free contact / no-nc type).

0 Answers   Max India,


Could anybody tell how much amps will a single input to plc will consume?

1 Answers  


what is meaning of static pressure

4 Answers   Ambuja,


Dear All can any one told me that VFD Make ABB Model ACS800-01 used for dual Source like 1.DC Source applied at terminal UDC+,UDC- 2. 3 phase 400AC,50Hz

1 Answers  


Control valve Flow characteristic. How the equal percentege curve form?

5 Answers  


Can I calibrate the Electromagnetic Flow Meter on line and How.

0 Answers   SEWA,


What is the standard height for stancion supports? and what is the standard mounting height for different transmitters?

11 Answers   Samsung,


wht is snap action switch?where it is used?is there any diff between snap action switch and normal pressure switch?

1 Answers   ONGC,


what is the diffrence between plc&dcs

4 Answers   HCL, Hindustan Zinc,


steam drum level transmitter calibration procedure? with example?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)