A DP Endress and Hauser flow transmitter is always tripping
pump at low flow. set point is 74 cubic meter/hr. Thorough
impulse line flushing and zero calibration has been done,
yet problem persists. What do you think is the problem and
how do you rectify this fault?
Answers were Sorted based on User's Feedback
The stated question assumes that the design criteria for a
low flow alarm SP at 74m^3/hr is valid. It is not clear
whether the problem is limited to the instrumentation
without a clear statement that the pump has been determined
to be operating properly. Since this is an instrumentation
exam, I'll assume the problem is in the instrumentation.
If the instrumentation is the problem, then the DP's
indicated DP/flow rate has to be lower than the alarm SP.
What can cause a DP transmitter to indicate a lower
DP/flowrate than it should?
If the equalizing valve is not tightly closed or leaks at
the valve seat, the DP will be lower than it should be as
the DP approaches zero, depending on the leak rate.
Damaged orifice plates read low, resulting in low indicated
DP readings.
Lower line pressure than the "design" line pressure will
reduce the indicated DP reading.
Someone changed out the orifice plate (OP)with an OP with
bigger bore or re-installed the correct OP backwards.
Since DP operation is "high side pressure minus low side
pressure equals indicated DP", a leak anywhere on the high
side will reduce the high side DP pressure and result in a
low indicated DP. That could be
- leak in the high side impulse line or its fittings
- manifold valve flange gasket leak on the high side or on
the process side
- vent leak
(however liquid leaks are usually visually evident)
In a mis-configured system, the PLC/DCS might have square
root extraction in addition to square root extraction on the
DP transmitter, which would cause a low flow rate indication
at the PLC/DCS.
Tell 'em Carl sent you.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / mohamed
You should see the time delay of the alarm itself and the time lag of the transmitter
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mukesh singh
increase the tripping time,your transmitter might be malfunctioning..follow the trend of DP.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ntia
Check the strainer of your pump..remember that your pump supplies the pressure...if the pump strainer is dirty...it will be be giving low flow and since your dp was set to shutoff the pump at a low flow..then your dp will continue to shut off the pump until the pump is cleaned and the fault is rectified.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / samir
If it is a malfunction of flow transmitter then you should cross check with portable ultrasonic flow transmitter. Whether it is showing correct or not. & then you can follow previous advise.
| Is This Answer Correct ? | 0 Yes | 0 No |
If a transmitter is installed 10 m below its tapping point how much pressure exerted if fluid is water?
how to solve temperature error in compressor?
What is the difference between HMI and SCADA?
TCD Principle
how to calibrate load cell
Explain plc level and its type?
WHAT IS DOPPLER EFFECT? WHERE IT IS APPLIED?
i want to know the interview format fot gail, instrumentation. pls answer me in habib.sami1003@gmail.com
how to calculate flow by dp transmitter?
What is the principle of a Pressure gauge?
why we take 4 to 20 mA as out put of every instrument like pressure transmittre ?why we cant take 0 to 20mA as output?
What is hp & mp seperator .& what is its working principle ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)