Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I want formula to calculate cable size as per load given in
kw & amp.I searched many sites but didn't right answer.Plz
reply me asap.

Answers were Sorted based on User's Feedback



I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / thiagarajan.e

motor full currentx1.25times to the nearest cablesize

Is This Answer Correct ?    0 Yes 0 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / babul

pls my need brb cable amp to watt formula to calculate

Is This Answer Correct ?    0 Yes 0 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / rajkumar mohan

For simple easy remembering...

Make ur own excel sheet as per below
(its strictly not a technical way)

for Eg:for breakers 10-100 dive the breaker value with 4.5 you will get some value go to thte next cable size

10A

10/4.5 =2.2sq.mm
go to 2.5 sq.mm
--------------------------

you can use this formula till you are familiar with the cable sizes (Y)

Is This Answer Correct ?    0 Yes 0 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / hosam

you have 100kva pole type TX
POWER 100x0.8= 80 kw
total load aprox: p= 47 kw
tx capactiy rate 47/100 =% 47 load
the resistance of earthing to be less than 3 ohms.
cable cu 70 squ mm to load 47 kw lengh 100 mtr
%e1= 0.0124(47x100)/70= 0.85 tolal load
from tx to panels supply 32.5 kw lengh 50mtr cable 4cxm35 mm squ + 14.5 kw lengh 25mtr cable10 squ mm
%e2= 0.0124(32x50)/35= 0.56
%e3= 0.124(14x25)/10= 0.4
%e = %(0.85+0.56+0.4)= %1,81 < %3
total of the voltage drop is acceptable

Is This Answer Correct ?    0 Yes 0 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / eng.saif.

Hi friends,
I want to exact formula of cable size and example ??? please anyone give me ans..........

Is This Answer Correct ?    0 Yes 0 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / safdar

dear.first we need to know about amp range.
example 50 amp which i have to select cable size according amp load.
amp range/5 up to 30 amp
and amp range / 4 up to 125 amp
more than it amp of range amp /2

Is This Answer Correct ?    0 Yes 0 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / abhishek gupta

For 400V 3ph AC system

# For 1% permissible voltage drop

size of cable in mmsq (aluminium cable)=( I*L) /80

# For 2% permissible voltage drop

size of cable in mmsq (aluminium cable)=( I*L) /160

# For 3% permissible voltage drop

size of cable in mmsq (aluminium cable)=( I*L) /240

I = Full load current
L = Length in meter from load center to motor

Is This Answer Correct ?    0 Yes 1 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / qasim riaz

sir plz send me proper formula for cable size calculation

Is This Answer Correct ?    0 Yes 1 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / tanu saxena

as u know power=v*i*power factor
the load is given in KW
SUPPOSE THE LOAD IS 30KW
FOR THREE PHASE VOLTAGE IS 440V
THEN, 30*1000=440*I*O.9(SUPPOSING PF)
30*1000=396*I
THEN, I=75AMP
FOR ALUMINIUM CABLE 1Sq.mm=1.5 amp of current
for copper cable 1sq.mm=5 amp of current
then, your cable size is 15sq.mm for copper cable

Is This Answer Correct ?    0 Yes 2 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / shine

it is easy,just refer some catalogue from a cable retail shop u idiot.

Is This Answer Correct ?    10 Yes 38 No

Post New Answer

More Electrical Engineering Interview Questions

briefly explain principle of resistance welding

0 Answers  


in the case of 6.6kv motor starter combination contain fuses on it VCB. but in 11KV motor starter combination Fuses are not using in it's VCB why?

0 Answers  


What is the GI Earth Flat Size recomended for 33KV 2000KVA Distribution Transformer

1 Answers  


Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?

4 Answers  


how to select fuse in any circuit? if with fomula ?and examples also

1 Answers  


what is the principle of dc generators?

7 Answers   CPCL,


The efficiency of a 100kva transformer is 0.98 at full load as well as half load , for this transformer what is the Copper loss at full load ?

0 Answers  


in power station power measuring unit is KW but in transformer is KVA why?

4 Answers  


how calculate external illumintion in a compound area. for e.g. there is one open park having 600m2 area and i have to put 40w flouresent tube fitting with pole. how shall i calculate the numbers of fitting.

1 Answers  


What is the diff btw Conventional & Addressable Fire Alarm System???

5 Answers   Emerson,


What is the difference between electrical earthing and electrical grounding?

0 Answers  


what is meant by switch fuse unit ?

3 Answers   Thermal Powertech Corporation India Ltd TPCIL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)