I want formula to calculate cable size as per load given in
kw & amp.I searched many sites but didn't right answer.Plz
reply me asap.
Answers were Sorted based on User's Feedback
Answer / amit kumar tripathi
PERCENTAGE OF VOLTAGE DROP IS EQUAL TO
% V DROP = 1.732*Ir*L/1000 ( R COSØ + X SIN Ø ) / V * N
WHERE
Ir = FULL LOAD CURRENT
L = LENGTH OF THE CABLE
R = RESISTENCE OF THE CABLE
X = REACTENCE OF THE CABLE
COSØ = 0.8
SINØ = 0.53
V = VOLTAGE
N = NO. OF RUN CABLE
MAXIMUM % VOLTAGE DROP CONSIDERED 6% As per IE Rule & it cable size designs is Economical.
If Power rating & required cable length is increase , so your cable size is also increase.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / muhammad usama qadir
you can calculate cable size by this link
http://www.solar-wind.co.uk/cable-sizing-DC-cables.html
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / tariqusman
if u want to find the cable size for a specific load. so u
find the load current. and just divid by 4, similsrly u
find the accurate size of cable for specific load. for
example. a load of 50kw, ist u find the load current, and
then divide by 4.
P = 50kw or 50,000watt
V = 440 volt
I = ?
p = 1.7320*440*I*0.8
I = p/1.7320*440*.8
I = 50,000/598.4
I = 83 Ampere
now u divid the load current by 4
83/4 = 20 sq.mm
its simple if u find the cbale size...
Is This Answer Correct ? | 10 Yes | 8 No |
hai am also no exact answer
may be
eg 5HP motor select cable size 2.5sqmm cu cable, r 4 sqmm
Al cable.
work out
5Hp motor taken 90% full load current 7 amps.
that current * 5 times = 35 Amps (motor not run in full load
its my experiance)
2.5sqmm cu cable full load withstand current 36A
4sqmm Al cable full load with stand current 34A
so we choice Cu r Al cable
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / sukhvinder singh
Kv*load/volt
for single phase use 230 volt& for three phase use 440 volt
Kv =1000
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / amit kumar tripathi
The Power Cable size shall be selected on the basis of
(a) Full load of Current Carrying Capacity
(b) Fault current Rating
(c) Steady state voltage drop
(a) Full load of Current Carrying Capacity
Transformer TRF-1 Rating (P) = 1600 KVA
Rated System Voltage (V) = 0.4 KV
Minimum size is required for full load current =P/_/3 x V
=2309.47Amps
Overall derating factor of multicore LV cables =0.660
From Cable catalogue, 1C x 400 Sqmm cable is selected and
Current rating of the cable in air = 680Amps
Therefore 6 cables Run is selected= 4080 Amps
Hence selected cable size is adequate
(b) Fault Current Rating criterion
Since feeder is protected by circuit breakekr, cable size is decided based on the bus of Fault current the transformer feeder .
The required size of cable for fault current is given by
formula =Isc. _/t
K
where,
Isc - Short circuit current in KA = 50KA
t - Fault Clearing time in seconds =1Sec
K - XLPE insulation factor = 0.094
Therefore required cable size = 531.91Sq mm
Hence, Actual cable size choose 6 Run - 1C x 400 Sq mm is adequate
(C) Steady state voltage drop
Ir - Full load current of motor = 2309.47Amp
Rated System Voltage (V)= 400V
Cos Ø = 0.85
Sin Ø = 0.53
L - length of the cable =5
N - No of cable runs per feeder =6 Run
R - Resistance of 1C x 400 Sq mm cable =0.104 Ohm / km
X - Reactance of 1C x 400 Sq mm cable =0.07 ohm / km
The voltage drop is given by formula =
√3 x Ir x L/1000 (R cosø1 + X sinø1)/N X V
Therefore voltage drop =0.1044 %
Voltage drop is less than permissible value of 6%
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / er. naushad ashraf
Dear See 1 eg. of Cable Designing
From - 5 MVA power T/f LV side
To - 11 kV LA’s
• RMS Symmetrical Short Ckt current = 17.39 kA (As per Tender spec.)
• Fault Clearing Time = 1 sec
• Min. Cable Size = (17.39x1000xsq root 1)/94= 185 sqmm.
• Min. Cable Size = 1-3C 185 sqmm.
• Cable Length = 0.06 Km. (Assumed).
• Ifl = (5000x1000)/(1.734x11000x0.9x0.95) = 307 A.
• Derating Factor = Ca X Cg = .88x1 = 0.88
• Cable sized considered = 3C X 185 sqmm. (XLPE+Al).
• Cable Resistance (Ohm/Km) = 0.21
• Cable Reactance (Ohm/Km) = 0.087
• Cable Ampacity = 330 A.
• Cable Derated Current = 330x0.88 = 290.4 A.
• Min. No. of cable required = 307/290 = 1.0586 = 1 No.
• No. of Cable Runs Selected = 1 No.
• % Voltage Drop = (sqrt 3x307x0.06(0.21x0.9+0.087x0.43)x100)/(1x11000)
= 0.066 % (Acceptable)
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / tariqusman
sorry i remind you that if u determind the above value of
cable size, for example i find 20 sq. mm cble for 83 ampere
load . so u use the 25 sq. mm cable.
sorry for 20 sq mm. there no have 20 sq.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / md. ekram ali
Ye sab galt jawab de rahe hai koi v correct answer nahi diya
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / naushad ashraf
As we Now that,
Area= (IscXrtT)/K, Factor for PVC or XLPE,
As we know that Derating Factor = AgXAaXAsXAf
and I= P/(rt3XVXCos#)
and I=DfXI
Is This Answer Correct ? | 0 Yes | 0 No |
My question is abt backlog.I had dropped one subject in my second year, and completed this subject in the 3rd attempt, so how many backlogs i have got?1 or 3?plz sujjest the answer as soon as possible
may anybody tell me the names of institute where plc programing course are conducted
why motor range is available 22kv,30kv,37kv,45kv and so on? why motor range is not available 21kv,24,25,26,27kv and so on?
Wat will happen if R-phase of an alternator is connected to B- Phase of AMF panel fed from alternator
what is die electric strnth of transformer ?
The error in a single phase energy meter where pressure coil lags behind applied voltage by 88 degrees and pf is 1) upf 2).5lag
Haw to check conductivity of budbar
What is cp system and why is it required.?
can a generator with 15AH specified battery for starting can be connected to a battery of greater capacity?
what is pilot wire? what is the use of pilot wires?
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
1ampear me kitna watts hota hai aur elcb ka pura naam kya hai
18 Answers Al Khayyat, Alpha G, BEC, Bhel, CGS, Electrical, Fiem, Firmenich, HLG Habtoor Leighton Group, Jash, Kandia, Maruti Suzuki, Minda, NTPC, ONEIC, Pace Process Controls, SMTC, SR, Sunrise Electrical, Sushil Enterprises, Suzlon, Voltage,