Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I want formula to calculate cable size as per load given in
kw & amp.I searched many sites but didn't right answer.Plz
reply me asap.

Answers were Sorted based on User's Feedback



I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / amit kumar tripathi

PERCENTAGE OF VOLTAGE DROP IS EQUAL TO
% V DROP = 1.732*Ir*L/1000 ( R COSØ + X SIN Ø ) / V * N
WHERE
Ir = FULL LOAD CURRENT
L = LENGTH OF THE CABLE
R = RESISTENCE OF THE CABLE
X = REACTENCE OF THE CABLE
COSØ = 0.8
SINØ = 0.53
V = VOLTAGE
N = NO. OF RUN CABLE
MAXIMUM % VOLTAGE DROP CONSIDERED 6% As per IE Rule & it cable size designs is Economical.

If Power rating & required cable length is increase , so your cable size is also increase.

Is This Answer Correct ?    3 Yes 1 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / muhammad usama qadir

you can calculate cable size by this link
http://www.solar-wind.co.uk/cable-sizing-DC-cables.html

Is This Answer Correct ?    4 Yes 2 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / tariqusman

if u want to find the cable size for a specific load. so u
find the load current. and just divid by 4, similsrly u
find the accurate size of cable for specific load. for
example. a load of 50kw, ist u find the load current, and
then divide by 4.
P = 50kw or 50,000watt
V = 440 volt
I = ?
p = 1.7320*440*I*0.8
I = p/1.7320*440*.8
I = 50,000/598.4
I = 83 Ampere

now u divid the load current by 4

83/4 = 20 sq.mm

its simple if u find the cbale size...

Is This Answer Correct ?    10 Yes 8 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / s.venkatraman

hai am also no exact answer
may be
eg 5HP motor select cable size 2.5sqmm cu cable, r 4 sqmm
Al cable.
work out
5Hp motor taken 90% full load current 7 amps.
that current * 5 times = 35 Amps (motor not run in full load
its my experiance)
2.5sqmm cu cable full load withstand current 36A
4sqmm Al cable full load with stand current 34A
so we choice Cu r Al cable

Is This Answer Correct ?    6 Yes 5 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / sukhvinder singh

Kv*load/volt


for single phase use 230 volt& for three phase use 440 volt
Kv =1000

Is This Answer Correct ?    4 Yes 3 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / amit kumar tripathi

The Power Cable size shall be selected on the basis of
(a) Full load of Current Carrying Capacity
(b) Fault current Rating
(c) Steady state voltage drop

(a) Full load of Current Carrying Capacity

Transformer TRF-1 Rating (P) = 1600 KVA
Rated System Voltage (V) = 0.4 KV
Minimum size is required for full load current =P/_/3 x V
=2309.47Amps
Overall derating factor of multicore LV cables =0.660

From Cable catalogue, 1C x 400 Sqmm cable is selected and
Current rating of the cable in air = 680Amps

Therefore 6 cables Run is selected= 4080 Amps
Hence selected cable size is adequate

(b) Fault Current Rating criterion

Since feeder is protected by circuit breakekr, cable size is decided based on the bus of Fault current the transformer feeder .

The required size of cable for fault current is given by
formula =Isc. _/t
K
where,
Isc - Short circuit current in KA = 50KA
t - Fault Clearing time in seconds =1Sec
K - XLPE insulation factor = 0.094
Therefore required cable size = 531.91Sq mm

Hence, Actual cable size choose 6 Run - 1C x 400 Sq mm is adequate

(C) Steady state voltage drop

Ir - Full load current of motor = 2309.47Amp
Rated System Voltage (V)= 400V
Cos Ø = 0.85
Sin Ø = 0.53
L - length of the cable =5
N - No of cable runs per feeder =6 Run
R - Resistance of 1C x 400 Sq mm cable =0.104 Ohm / km
X - Reactance of 1C x 400 Sq mm cable =0.07 ohm / km
The voltage drop is given by formula =
&#8730;3 x Ir x L/1000 (R cosø1 + X sinø1)/N X V
Therefore voltage drop =0.1044 %
Voltage drop is less than permissible value of 6%

Is This Answer Correct ?    4 Yes 4 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / er. naushad ashraf

Dear See 1 eg. of Cable Designing

From - 5 MVA power T/f LV side

To - 11 kV LA’s

• RMS Symmetrical Short Ckt current = 17.39 kA (As per Tender spec.)

• Fault Clearing Time = 1 sec

• Min. Cable Size = (17.39x1000xsq root 1)/94= 185 sqmm.

• Min. Cable Size = 1-3C 185 sqmm.

• Cable Length = 0.06 Km. (Assumed).

• Ifl = (5000x1000)/(1.734x11000x0.9x0.95) = 307 A.

• Derating Factor = Ca X Cg = .88x1 = 0.88

• Cable sized considered = 3C X 185 sqmm. (XLPE+Al).

• Cable Resistance (Ohm/Km) = 0.21

• Cable Reactance (Ohm/Km) = 0.087

• Cable Ampacity = 330 A.

• Cable Derated Current = 330x0.88 = 290.4 A.

• Min. No. of cable required = 307/290 = 1.0586 = 1 No.

• No. of Cable Runs Selected = 1 No.

• % Voltage Drop = (sqrt 3x307x0.06(0.21x0.9+0.087x0.43)x100)/(1x11000)
= 0.066 % (Acceptable)

Is This Answer Correct ?    2 Yes 2 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / tariqusman

sorry i remind you that if u determind the above value of
cable size, for example i find 20 sq. mm cble for 83 ampere
load . so u use the 25 sq. mm cable.

sorry for 20 sq mm. there no have 20 sq.

Is This Answer Correct ?    2 Yes 2 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / md. ekram ali

Ye sab galt jawab de rahe hai koi v correct answer nahi diya

Is This Answer Correct ?    0 Yes 0 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / naushad ashraf

As we Now that,

Area= (IscXrtT)/K, Factor for PVC or XLPE,

As we know that Derating Factor = AgXAaXAsXAf

and I= P/(rt3XVXCos#)
and I=DfXI

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

This is reqd for a 1MW Solar power plant..We have 2DC outputs from the solar panels Connected to 2INVERTOR panels.. Output from invertor is 3ph,280v,500kva,50hz.These are connected to individual ACB.This has to be stepped up to 11KV ,1250KVA SYSTEM.Now can I use (1) one more ACBTO GIVE A COMBINED OUTPUT OF 1000KVA,280V & STEP UP THE OUTPUT BY USING a single two winding 3 ph transformer 11kv/1250kva. or (2)use the two outputs and connect to one three winding transformer of above rating..Pls suggestwith details.

0 Answers  


why we use star connection in HT motor? and delta connection in LT motor

2 Answers   npcc,


I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.

0 Answers  


CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND TAKING OUTPUT FROM PRIMARY?

3 Answers  


why capacitor using the induction motor?

6 Answers   Kirloskar,


How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f used in Canada is to be operated on 50 hz in Europe frequency then how will its KVA rating change? a-increase b-decrease c-remains same

1 Answers  


why needtwo winding LV and HV in transformer?

1 Answers   Organic Industries,


What are thermo couple cables and where they are used.

2 Answers  


why not phase to phase fault occure in raining day in hv sub-station?

1 Answers   Getco,


what is difference between vcb and mccb

4 Answers   APTransco,


what is the significance of positve n negative voltage regulation .on alternator

1 Answers   TCL,


HOW TO CALCULATE EARTHING SIZING?

0 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)