AT THE TIME OF INSTALLING THE POWER PLANT POWER IS TAKEN
FROM NEARBY GRID AND GIVING THE SUPPLY TO THE GENERATOR
WHICH ACTS AS MOTOR. WHAT IS THE NEED OF RUNNING THE
GENERATOR AS MOTOR?
Answers were Sorted based on User's Feedback
I think The question who have asked, wanted to ask that "AT
THE TIME OF START-UP A POWER PLANT....." & NOT "AT THE TIME
OF INSTALLING THE POWER PLANT ...."-------------If my above
assumption is true, then the answer WILL BE as follows :-
TO BRING THE GENERATOR NEAR TO SYNCHRONUS SPEED DURING
START UP.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / natrajan tt
normally nobodies given to the supply directly to the
generator.In a power plant installation time they are drawn
supply from grid and given to the step down transformer like
11kv/430v for boiler and turbine auxiliaries startup use,
otherwise if ur possible to giving the supply to generator
it will act like a motor.Breaker capacity & Cable size or no
of runs to be added.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / venkatesan.j
In a gas power plant during initial light up the generator
is acted as motor to run the compressor to produce the
necessary air for compustion in combustion chamber.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / s.p.p.pathirana
The perpose is connecting grid power to the power plant
generators for syncronized both the system such as
(volt,freqency,and phase sequence)generator or alternator
has coupled to the engine. according to the question that
motor will turn engine to the oposite derection and engine
may damaged. there for generator have protection system to
prevent this. its call reverse power protection. power
plant for support to the grid and have connected grid power
cable to the generators through individual there circuit
breakers. generator breaker cannot close with engine
standby mode. if this correct please try to understand.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ashish patil
In order to produce residuual magnitism there is seperate
exiter so there is no need to run generator as motor.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / dayal varma
to chek the capacity of the cables and winding of the
generator are able to work in such a high power
| Is This Answer Correct ? | 2 Yes | 8 No |
In 3.5X150 Sq.mm cable what does 150 stand for outer dia or inner dia?
is EEE eligible for getting electrical supervisor certificate ? if yes then from which state i sud apply
difference between ordinary MCCB & Motorised MCCB
WHY THE TRANSFORMER VALUE MEASURES IN KVA INSTEAD OF KW.
WHAT IS THE SIGNIFICANCE OF VECTOR GROUPS IN TRANSFORMER? WHAT WILL BE EFFECT WHEN PHASE DISPLACEMENT CHANGES IN TRANSFORMER?WHAT IS THE NEED TO BE PHASE SHIFT CHANGE BETWEEN THE PRIMARY AND SECONDARY WINDING
what things to be considered when designing UPS
0 Answers Aplab, Veta Kipawa ICT Center,
what is the use of interposed & reverse voltage transformer
what is load cell
what is the Excaste meaning of CT Saturation?? 10 P 20, 15 VA, what is the meaning of 10, & 20. if the CT polarrity changed what will happened?? what is the differece between measuring CT & Protection CT?? what is the Saturation Point of measuring CT & Protection CT??
WHAT IS A LINE CURRENT AND PHASE CURRENT
Why star pointed terminal have no current? how?
what is the full form of KVAR
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)