what is reason in mv breaker the control supply voltage is dc not ac?
Answer / surajit mishra
A Circuit Breaker is often required to operate when there is no power. If the auxiliary power in a station is taken for the Main power supply, the CB Trip coil and closing coil will not have power to operate. The CBs have Closing Coil for switching On and a Shunt Trip coil for switching off. In substations, DC Control supply, usually 110V DC, from Lead Acid Battery sets are maintained to provide DC supply for operating the Closing Coil and Trip Coil. Not only MV Breakers, if the system requires even an LV Breaker to operate when mains power is not available, DC Control supply is used.
Is This Answer Correct ? | 0 Yes | 0 No |
Define reserve-generating capacity?
explain safety measures in alternator?
what is meant by lagging & leading current
what is the working principle of contactor and conditions of normal open and normal close on it?
WHAT WILL BE THE SPEED OF MOTOR IF NO.OF POLES ON STATOR ARE NOT EQUAL TO NO. OF POLES ON ROTOR.???
What is the working of AVR in AC generators?
13 Answers Navrachana University,
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
electric contractor ya contactor kia hota hy ? or kesy connect kia jata hy ?
can anybody send me syllabus of rrb section engg (electrical). and also send previous question pepar...
WHAT IS THE CONDITION FOR OPERATING DIFFERENTIAL RELAY IN POWER TRANSFORMER & WHERE IS NEUTRAL CT PLACED IN TRANSFORMER
what are the types of cables?
what is cogging and crawling
20 Answers ABB, Ashok Leyland, Bharat Bijlee, BMRCL, MN Dastur, Siemens,