why transformer does not obey ohm law?..

Answer / blueraja

I'd also like to mention (sorry, there is no "edit" button)
that transformers absolutely **DO** obey Ohm's law - this
apparent contradiction does NOT occur because, as some have
stated above, "transformers are non-ohmic devices." This is
simply not true.

Is This Answer Correct ?    2 Yes 1 No

why transformer does not obey ohm law?..

Answer / blueraja

@Nishant: I apologize, the blog post I mentioned above
(answer #13) is down - I promise I will get it back up
within the next week to answer your question.

The quick-and-dirty answer is that Ohm's law tells you how
voltage and current relate in a single circuit, while the
power-conservation-law-for-transformers tells you how a
transformer relates voltage and current in two separate
circuits.

For a more in-depth explanation, refer to my blog post in
answer #13 in about a week :)

Is This Answer Correct ?    0 Yes 0 No

why transformer does not obey ohm law?..

Answer / nandakishore

Transformers obeys ohm's law.transformer consists of two
circuits primary and secondary both circuit obeys ohms law
but when the are magnetically coupled they obeys power
conservation law.the variation in the current or voltage is
due to resistance value

Is This Answer Correct ?    0 Yes 0 No

why transformer does not obey ohm law?..

Answer / manmohan

but you did not mention about the change in temparature?to
satisfy the ohms law,temparature must be constant?how do you
justify ur answer?

Is This Answer Correct ?    0 Yes 0 No

why transformer does not obey ohm law?..

Answer / ad patel

In ohm's law resistance is constant.
In transformer resistance is change with changing in voltage,because voltage is change by changing the length of winding.....
So in transformer R is change so here the Joule's temperature law is apply..
Where Joule's law is follow there ohm's low is not follow....

Is This Answer Correct ?    0 Yes 0 No

why transformer does not obey ohm law?..

Answer / n.rajasekhar

thats because of induced voltage in the winding,but finally
while applying ohms law see how much net voltage appearing
across the impedance.just take one numerical example and see
you will get it.

Is This Answer Correct ?    3 Yes 4 No

why transformer does not obey ohm law?..

Answer / surender rawat

A transformer is a device that transfers electrical energy
from one circuit to another through inductively coupled
electrical conductors. A changing current in the first
circuit (the primary) creates a changing magnetic field.
This changing magnetic field induces a changing voltage in
the second circuit (the secondary). This effect is called
mutual induction.

The e.m.f. required to drive electrons across inductive
and capacitive loads vary depending upon the powerfactor
at which the load is designed. The power factor in case of
resistive load is 1 and always remains so. Also, for change
in e.m.f., L and C loads receive varying responses. In
case of resistive loads, the response is steadier for a
longer duration compared to capacitive or inductive loads.

Is This Answer Correct ?    8 Yes 9 No

why transformer does not obey ohm law?..

Answer / daher

ohms law applied to electric circuits wathever it AC or DC
CIRCUITS,V=IR or V=IZ where Z=(R^2+omegal^2)^1/2.the
equivalent circuit of transformer is composed of resistance
and inductance and ohms law helps to solve the problem

Is This Answer Correct ?    3 Yes 4 No

why transformer does not obey ohm law?..

Answer / krish

Ohms Law applicable in constant Temperature condition only. But in Transformers we can't maintain constant Temperature in primary and secondary so it doesn't obey Ohm's law

Is This Answer Correct ?    1 Yes 2 No

why transformer does not obey ohm law?..

Answer / dr h

I think there is a fundamental misunderstanding here. Ohm's law is just a statement that says that current is proportional to the applied voltage across a resistor at constant temp.

The resistance is defined as the ratio of voltage to current at any instant and this happens to be constant for all current voltage values at constant temp. For a filament lamp this ration changes as temp changes.

With a transformer secondary coil you cannot just consider the resistance of the output coil as you are dealing with alternating current, which leads to capacitive and inductive reactance. You are generating whats called back emf, defined by Lenz's law, which is ultimately a statement which results from the conservation of energy.

Considering the case of a step up transformer, somebody with a basic knowledge of electricity will question how that can be since the resistance is the same and the voltage has increased but yet the current has decreased. This is because the output resistance is still exactly the same but its imput impedence has increased. When dealing with AC voltages, you need to talk about the impedence, which only is partly due to the resistance.

It can be very confusing, but studying the physics of AC circuits should help you understand. Ultimately it is due to the conservation of energy, which will hold at all times and in all situations.

Dr H

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

why can tv operate at low voltage??

2 Answers  


what is the major difference between dc generator and synchronous generator?

4 Answers  


which type of motor is suitable for lift?

18 Answers   NTTF Nettur Technical Training Foundation, Pothigai Power Solutions,


how can check the resistance of battery contact?

0 Answers   Cipla,


Why Aluminium wires are used for High tension(HT) lines? 11 KVA/32KVA & aboue

6 Answers  






If we know the load for generator in KW then how it will be change to amps and also if we know the load in amps how it will change in KW and what Generator is good for that...suppose load is 500 amps 3phase......??

1 Answers  


how many number of terminals are available in CURRENT TRANSFORMER

6 Answers   MSETCL Maharashtra State Electricity Transmission Co Ltd,


If R and Y terminals are short circuited,then power will cut. we all know that power cannot be stored.what will happen to already generated power at power station?

3 Answers  


how i decrease the neutral to ground voltage , thats i read 7v on my digital meter.i dont know about my earth pit.

2 Answers  


There are a Transformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?

4 Answers  


what is the use of terminals in transformer ?

1 Answers   Core Solutions, Honeywell,


What Is Sampling?

0 Answers   Mahatma Gandhi University,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)