Answer / anjireddy boduggam
VCB - vacuum ckt. Breaker , Quenching medium - Vacuum,
ACB - Air ckt. Breaker , Quenching medium - Air,
OCB - oil ckt. breaker , Quenching medium - Oil
above in all ckt. breakers different quenching medias are
using.
The above all ckt. Breakers principle is same, but medias
are used for arc quenching purpose.
OLR - over load relay , when current exceeds over setting
point, then action will be started and disconnected the
load supply by relay action.No medium is used in the OL
relay, but it works on bi-metallic action.
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / zubair
ACB MEAMS AIR CIRCUIT BREAKER.
VCB MEANS VACCUM CIRCUIT BREAKER.
OCB MEANS OIL CIRCUIT BREAKER.
ALL THE ABOVE USED TO TRIP THE CIRCUIT,WHEN EVER THEIR IS A
FAULT AT THE LOAD SIDE, like short circuit,excess current
consumption beyond the rated value
THE DIELECTRIC STRENGTH OF VCB IS HEIGHER THAN ACB.THE ARC
EXTINGUISHER CAPACITY OF VCB IS HEIGHER THAN ACB.HENCE VCB
IS USED FOR HIEGHER VOLTAGES AND RATINGS.
THE OLR(OVER LOAD RELAY)IS ALSO USED TO TRIP THE
CIRCUIT ,WHEN EVER THE LOAD TAKES HIGER CURRENT BEYOUND
RATED VALUE, BUT THE APPLICATION IS LIMITED TO 20A.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / sanjay kumar
Transformer Mai oil konsa hota Hai Transformer oil temperature winding temperature kitna hona chahiye on load
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / priti ranjan mohapatra
V.c.b - it stands for vaccum circuit breaker. It used in mv line as 36, 33 kv. In this the contact point of the cb remains in vaccum when it is off.
| Is This Answer Correct ? | 8 Yes | 8 No |
what will be efficient rating of ac motor to lift a 10 kg wt of stone to 10 meter height with input 220V AC 50 Hz frequency???
HOW WE KNOW IN PHYSICALLY THE CONTACT SURFACE OF A VACUUM INTERRUPTER IS GOOD OR GOING TO DAMAGE IN A VCB AFTER ABOVE 500 TIMES OPERATED.
what is meant by bus bar and outgoing/incoming breaker in an electrical/electronic circuit
In generation,transmission and distribution voltage frequency is either 50HZ or 60 HZ;why are only these frequencies?
can transformer of different kvas be paralled
if we apply 1000ADC instead of 100ADC or We apply 50ADC instead of 100ADC,What will be happened in the test result value.Pl explain
why resistive load has unity power factor,inductive load lagging and capacitive load leading power factor?
When we giving the 3 phase supply to ups system how to coming netural?
0 Answers Juniper Networks, Tata Motors,
comparision between mcb,mccb,elcb,flcb,elcb in details
how many types are their in switchyard or substation(like D,I TYPE), what is differant between them
WHAT IS DGA TEST FOR THE TRANSFORMERS.
what is d meaning of inrush current of a trafo ? how u can calculate this ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)