how to choose the cable rating for load (KW)? EXAMPLE.50KW load
Answers were Sorted based on User's Feedback
Answer / er.p.somasundaram
1 H.P = 1.25 Amps
IN CASE ALUMINIUM CONDUCTOR USE CONSTANT VALUE IS =0.75
IN CASE COPPER CONDUCTOR USE CONSTANT VALUE IS =1.25
SO CONDUCTOR SIZE= 1.25*1.25(CU)=1.25SQMM
| Is This Answer Correct ? | 26 Yes | 35 No |
Answer / er.p.somasundaram
10 H.P = 10.25 Amps
IN CASE ALUMINIUM CONDUCTOR USE CONSTANT VALUE IS =0.75
IN CASE COPPER CONDUCTOR USE CONSTANT VALUE IS =1.25
SO CONDUCTOR SIZE+cable sqmm *075 =10.25amps, now a days increase current so cable size is small size increases.
10.25*0.75=10 sq mm
| Is This Answer Correct ? | 15 Yes | 33 No |
Cable carring capasity is there.. we can get form cable
manufacturer...
for 50kW load,
current(I) = 50/(1.732*415*.8(p.f))
I = 28.75A
For 1.5Sqmm cable curent carring capasity = 20A in ground
2.5 = 27,
4 = 34,
6 = 43,
10 = 57,
16 = 73A like that.
now our load current is 28.75A
No.of cable with size =28.75/43A (6Sqmm)
= .6686/.7 (Diff factor)
=.955
there fore 1run 6 Sqmm aluminium cable we selected for 50
kW load.
| Is This Answer Correct ? | 31 Yes | 153 No |
Answer / suresh kumar
Copper Cable: Sqmm*1.5, Exam: If we have 50 Sqmm copper
cabe, The it will take load is 50*1.5=75Amp
Al Cable is multiplying factor of 1.
Exam: 50 Sqmm cable will take 50A load.
| Is This Answer Correct ? | 98 Yes | 233 No |
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test. why transformer rating in always in KVA ? what ispositive, negative, zero sequence impedence? How ElCB tripping if Neutral touch with ground Why AC & DC capacitor are use in UPS ? why motor rating in KW? how to syncronize two dg sets
HOW TO DRAW THE VECTOR DIAGRAMS OF A Dyn 11,YdN 1 transformers?
explain remenance . differentiate high remenance type ct & low remenance type ct
What is the difference between analogue electronics and digital electronics?
Can run 11KV(5MW) slip ring motor by appling 415V? if Yes and what are the processors?
what is the max working temperature of an oil filled transformer say of about 1500kva.
What is the rating of your substation and what are the different types of substations?
only some transformers and some generator requires NGR why?
why we maintain 50hz ,220volts,20Amp,ratings fixed every where in india,,electricity
whate is aelectrical power fector for exampal
why we measure output of transformer in kva?
what is static electricity and how it generates?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)