what is the effect of power factor on DG supply,i mean to
say what will the effect if we add capactors on dg supply.
Answers were Sorted based on User's Feedback
Answer / sachin
there will not be an effect on DG if we add the capacitor.
But normally we recommend to install capacitor bank where
load is fluctuating, unstable.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / mahavir jagdev
The capacitor bank is kept to improve the power factor as most of the industrial load is inductive, hence to get the power factor to close to 0.85 or more the caoacitor bank helps. thus reduing losses.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / praveen yadav
yes we can, but it can be upto safe life limit of extent of 0.95 P.F Usually dg set are designed over 0.8 P.F.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sumanth aptransco
idon't no about DG.in dc supply has no pf (unity).suppose we
connect c in dc it acts a open ckt.
| Is This Answer Correct ? | 1 Yes | 5 No |
In the market there is availability of MCCB & ACB (800A), So, Where i can use MCCB & ACB for the same Rating?
There is 3phase power cable from 1 point to the other point which is 100m away. Two point equipped with power meter and recorded 1st point is 205kW while the 2nd is 202kW and each phase average carry 400amps. To calculate the resistance of the 3phase power cable, is the formula using will be P=I2R?
Can We Apply DC POWER To Transformer???? And Why????
why celing fan is running in anti clock wise and table fan is running in clock wised?
mention hazard experienced during installation
How the over load setting for HT Motors calculated-provided in Numerical Relay
0 Answers Damodar Valley Corporation,
We are planning to synchronized DG's with our captive plant in the event of black start of plant, but before sync we checked voltage of DG with our plant voltage and it varies from 5 V to 450 V. So in this condition how we can sync DG with plant ?
What is the difference between Class PX & Class X CT's
Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?
What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?
Load 380kva eb 415v,load amps 350.Same load dg 415v,load amps 420 what reason ?
1 Answers AVT Natural Products,
What is the maximum advisable distance where it is required to interconnect a 500 KVA 480 V 3 ph transformer and the main panel or MCC ignoring the voltage droop affectation, does it is exist any standard about it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)