can i know how to design overcurrent setting and earth
fault for 11kv & o.433kv system assuming tx 1000kva.
Answers were Sorted based on User's Feedback
Answer / prakash.
First selected for ct ratio in HT panel.1000kva transformer full load current in primary 52.5amps.so ct ratio in 60amps(60/5).
Now relay setting for over current 55amps.
And earth fault setting 0.5amps in ct secondary amps..
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
Normally EFR is set at 20% 0f OCR setting.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is diffrential relay used in generator plz give brief explanation
i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star connection at both side.but it have another thied winding tertiary winding.what is used of this winding. pl tell me
what is the function of choke and starter in a tube light??
what will hapen if secodery circuit is open of current transformer WHy neutral to ground trips when neutral touches the ground
Ratings of power transformer,Distribution transformer.
WHERE CAN I GET THE PREVIOUS QUESTION PAPERS OF Govt Polytechnic in deee 2nd year papers
Why inverter rating in KVA?
is it possible to turn on the single phase star delta on delay timer using 24 v dc ?
Explain the working principle of Synchronous Generator and Assynchronous generator?
What is diode fuse ? How it is working?
how to deside the capacity of chock for drive?
what is an S.C.R. and how do they work?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)