can i know how to design overcurrent setting and earth
fault for 11kv & o.433kv system assuming tx 1000kva.
Answers were Sorted based on User's Feedback
Answer / prakash.
First selected for ct ratio in HT panel.1000kva transformer full load current in primary 52.5amps.so ct ratio in 60amps(60/5).
Now relay setting for over current 55amps.
And earth fault setting 0.5amps in ct secondary amps..
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
Normally EFR is set at 20% 0f OCR setting.
| Is This Answer Correct ? | 2 Yes | 0 No |
If VFD is On but no starting commond on it. so how many outpout voltages of VFD
HOW DEFINE THE IP FOR ELECTRICAL EQUIPMENT AND WHAT IS THE IP OF PANELS USING IN HAZARDOUS AREA ?
why a three phase transformer cant rotate like three phase motor
WHY WE CAN GENERATE POWER IN 3PHASE MODE ONLY NOT IN 4 OR 5 PHASE?
what is the function of choke in tube
A circuit breaker on detecting fault will a. Open b. Close c. Open and trigger the alarm
On what basis no of earth pits are to be decided either for transformers or for equipment?
What is center gravity load in substation?
why we need to us lenz's law for synchornous motor
WHY PROTECTION CT IS USED NEXT TO METERING CT?
What is Isolation Current transformer and what purpose to use it in REF relay ?
At what condition differential relay will act in transformer and ht motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)