I need to calculate the Battery bank back up for below configuration:-
UPS - 120 KVA
Battery Bank - 200Ah
Volt of each cell - 12 V
Total No of cell - 34 No's
Can you please help me to get the battery back up time for above configuration...? along with formula
Energy stored in each battery = 12 x 200 WH ( VAH) ,total stored energy = 12 x 200 x 34 WH . Divide this by load in W to get ' Back up time' in hours (approx)
| Is This Answer Correct ? | 0 Yes | 0 No |
why it is not advisable to run low rating (19KVA) DG sets in parallel for long durations even though they are provided with droop ckts (QDC)
up to what extwnt of voltage the celing fan works?
What should be the conservator minimum oil level required in 2 mva transformer
in a simple IDMT relay we use neutral point of ct for earth fault then what is the requirement of neutral ct and cbct?
how the capacitance is caluclated if the load is varying to keep the power factor constant(above0.95)
Why does capacitor block dc supply?
What effect of supplying stationary generator (800kVA) with 415V AC from 1500kVA transformer?
what r the tests on the 3 phase transformers can any one explain how to test using megger on transformers thx
what is impedance of transformer?
7 Answers Synergy, Vijai Electricals,
why the impedence of the transformer is expressed in percentage?
one hp 3phase motor what generate power factor
How may I get the maximum current capacity for a particullar size Alluminum or Copper cable if there is compulsion to use?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)