I need to calculate the Battery bank back up for below configuration:-
UPS - 120 KVA
Battery Bank - 200Ah
Volt of each cell - 12 V
Total No of cell - 34 No's
Can you please help me to get the battery back up time for above configuration...? along with formula
Energy stored in each battery = 12 x 200 WH ( VAH) ,total stored energy = 12 x 200 x 34 WH . Divide this by load in W to get ' Back up time' in hours (approx)
| Is This Answer Correct ? | 0 Yes | 0 No |
For an 100kw generator, only 50kw of load is connected. will the generator generate only 50kw or 100kw. if it generate 100kw what happens to rest of the 50kw. what happens if we connect more than 100kw of load?
why the three phase transformer's star point does not sparks or seperated? while we often see that two phases touches each other it sparks and ocationaly conductor breakes out.
2. What are the parameters of EHT sub-station?
What is the equivalent circuit of a transformer and its vector diagram?
3phase cable calculation formula by motor load
why frequency should be constant?
Is it posible to instal one more SMDB from the existing SMDB and is it practical.
what is the maintaining Cf in UPS.
1. Why a DC motor starter is called 3 point starter
21 Answers ABB, CG, College School Exams Tests, Crompton Greaves, Infosys, Siva,
What is the difference between synchronous motor & asynchronous motor
Is LV shorted in magnettic balance test?If yes why?
How may I enrol or get admission to your program?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)