what is derated current of power cable & what is formule to
find derated current?
Answer / mahesh sali
See , the formula for derated current is nothing bu derated
factor .
Mostly derated factor depends upon the following points.
Way of cable laying i.e. on cable trays / duct / pipe etc(
open to air or into the Hume pipe or under ground )
Cable laying by grouping & having distance between two
cable as per individual manufacturer recommandation .
Each manufacture gives the deration factor for the above
stated point.
Deration means your cable carry the less current below your
rated capacity due the above reason.
take example.
suppose
1.5 sq.mm. cu carrying the current around 12 amp.in open to
air at 25 deg.c ref. temp. as per cable manufacturer
after considering the above stated point
if suppose my deration factor would be around 0.6
then deration current of above cable would be - 12 *
0.6=7.2amp
it means that your cable carry the less cuurent do the way
of laying , temp. cable grouping etc.
i hope above inf. sufficient for understanding
thanks
| Is This Answer Correct ? | 11 Yes | 3 No |
why does not tester light up when it is touched to neutral of 3 pin socket.
what happen if the supply is given to the stator of the 3phase induction motor with out assembling the rotor ?
What is power factor?
In a 3 phase,400v,4 wire system, 2 incandescent lamps, one having 230v,100w and the other 230v,200w are connected between r phase- neutral and y phase-neutral respectively. If neutral wire breaks which lamp will fuse first and why?
How short circuit MVA(Fault MVA) in a power system calculated for calculating number of earth plates ?
What is the difference between power,voltage,current? and with example
what is the principal of ceiling fan and how it will rotates? what is the magnetic momentum produces inside the fan?
What happened to installed high capacity conductor for smaller current rating?
How time response of the system is divided?
Pls tell me whether we can use EN3A material for shafts of Permanent magnet alternator.What will be the effect of magnetic and nonmagnetic material for shafts on magnetic properties of PM rotor .
State the function of control rods used in nuclear reactor
Why we apply only reduced voltage to the alternator while conducting slip test ? also the current increases to a larger value with reduced voltage itself Why ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)