what is derated current of power cable & what is formule to
find derated current?
Answer / mahesh sali
See , the formula for derated current is nothing bu derated
factor .
Mostly derated factor depends upon the following points.
Way of cable laying i.e. on cable trays / duct / pipe etc(
open to air or into the Hume pipe or under ground )
Cable laying by grouping & having distance between two
cable as per individual manufacturer recommandation .
Each manufacture gives the deration factor for the above
stated point.
Deration means your cable carry the less current below your
rated capacity due the above reason.
take example.
suppose
1.5 sq.mm. cu carrying the current around 12 amp.in open to
air at 25 deg.c ref. temp. as per cable manufacturer
after considering the above stated point
if suppose my deration factor would be around 0.6
then deration current of above cable would be - 12 *
0.6=7.2amp
it means that your cable carry the less cuurent do the way
of laying , temp. cable grouping etc.
i hope above inf. sufficient for understanding
thanks
| Is This Answer Correct ? | 11 Yes | 3 No |
If DG runing time Neutral earth connection Dissconect what will be the effect in load and equipments.
If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor rating accordingly.Illustrate by showing formula?
I am new guy as an electrical engr. in a 100MW HFO based power project. I am in operations division. I have noticed from last few days, my supervisor sends the last 24 hours energy generation calculation to my plant manager. I have noticed, he calculated last 24 hour's generated energy differences in KWH then he multiplied it with a multiplying factor 960. for example: total difference =2.685 KWH*960= 2577.6 MWH. but he does not not know what is multiplying factor 960?? can anybody explain it??
How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?
what is the max working temperature of an oil filled transformer say of about 1500kva.
I have a 1000 kVA Transformer(11kV/0.415kV) and a APFC panel of 400 kVAR(LT).Now if i want to remove the LT APFC panel and install a HT(11kV) APFC panel on the HT side is the HT APFC panel will work same as the LT APFC panel(improve the power factor),if yes what will be rating of the HT APFC panel?what is the formula to calculate HT APFC panel rating???
ACB & VCB how do work and saftes and how can maintenance in this and parts name show with picture
What are protection of transformer on HT side & on LT side?
Explain about how is it working Earth fault'relay and wahts the resistance value of earth bed
DG Earth Value?
0 Answers Reckitt Benckiser, Vodafone,
how actually an anti pumping device works? what is the operational principal?
what is meant by transformer oil temparature
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)