Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how much loading in terms of ampere can put on 5 MVA,33/11
KV TRANSFORMER having rated current 263 Amp ?????????

Answers were Sorted based on User's Feedback



how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / sunil bhuarya

its sunil bhuarya
ans of this question is ut self in the que.
how-
5000/(root3)*11=262.43 aproxx=263
and in case of overloading it becomes 300 to 315A.

Is This Answer Correct ?    38 Yes 7 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / ynrao

263 Amps as the question itself says

Is This Answer Correct ?    29 Yes 7 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / serwox

Answer depends on what percentage overload a transformer can
accept. For a tx that can accept a 120% overload, the
current is 315A.

Is This Answer Correct ?    20 Yes 5 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / pravin

Actually it depends upon designer. If we asked designer to
designed for 125% overload, he will provide cooling per
current loading on 125% overload to restrict Hot Spot Temp.
of the winding & Top oil temp. respective to max. ambient
temp.
In this case, we can provide loading of 437A in
terms of ampere on top rating with Hot spot temp & top oil
temp in control on top rating. Actually transformer has
three rating OA/FA/FA. If this transformer is OA/FA/FA then
we can provide this loading.
If it is self cooled then 263A is max. loading.

Is This Answer Correct ?    5 Yes 1 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / sunil kumar das

above answer is also correct.we can put less than full
load current.

Is This Answer Correct ?    6 Yes 3 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / jayant subhash golait

If the word rated current comes,then it is actually safe n maximum permissible limit....Obviously,the machine will misbehave when crossed this limit...to save the machine or to avoid failures,extra cooling may be required that is also within tolerable range...again the manufacturer may declare that value as a rated current which is itself little bit away from tripping or breakdown or danger zone of tolerance....finally ,it is solely depend upon manufacturer n in turn the quality of raw material used to design the machine....

Is This Answer Correct ?    1 Yes 0 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / narayanan surendran

The question did not talk about cooling and Tap Changer Type.
If over loaded, voltage drop and over heating may occur.
Therefore given rated current 263 A is correct.

Is This Answer Correct ?    0 Yes 0 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / sam

That depends on the rated output's power factor and the
load power factor.

Is This Answer Correct ?    2 Yes 3 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / har

300amp

Is This Answer Correct ?    8 Yes 10 No

how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263..

Answer / pankaj

Normayy transformer gives max efficieny at 75% of its rated
capacity because in that case cu loss = iron loss.

Is This Answer Correct ?    1 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

fog produced due to?

2 Answers   MAHINDRA,


What are the weight of 800KV DA,DB and DC type tower ?

0 Answers   L&T,


How do I calculate/select Droop CT ratio for various capacity of generators?

0 Answers  


In a star-star connected h.t transformer why we use NGR on the secondary (l.t)side.

3 Answers   Star, TATA,


electricity board have asked me what size meter i need fitted in my garage, its a 415volt supply and i want to run six 20amp supplies tolifts and things plus ten florry lights , what kva meter do i need??

2 Answers   HCL,


why dc supply is given to the field of alternator

9 Answers  


what is the earth resistance

4 Answers   Micron Electricals,


why square root 2 is multiplied with line voltage in selection of LA ie 11/sqrtroot3=6.35 kv and it is multiplied with sqrt2 ie 6.35 KV*sqrt2=8.9 kv we will select 9kv.my question is why we are multiplying with sqrt 2?

1 Answers   KSPL,


what is the slip of synchronous motor

1 Answers  


What is the exact load current needed for a place which has 100nos of bulb of each 100w?

2 Answers  


how can get electrical "c" licence.i am complited in DEEE.PASSING YEAR OF 1993.WORKING IN PVT COCERN LT LINE.PLEASE ADVISE ME .CELL NO 9994786021

0 Answers  


why corona loss is less with negative polarity?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)