how much loading in terms of ampere can put on 5 MVA,33/11
KV TRANSFORMER having rated current 263 Amp ?????????
Answers were Sorted based on User's Feedback
Answer / sunil bhuarya
its sunil bhuarya
ans of this question is ut self in the que.
how-
5000/(root3)*11=262.43 aproxx=263
and in case of overloading it becomes 300 to 315A.
| Is This Answer Correct ? | 38 Yes | 7 No |
Answer / serwox
Answer depends on what percentage overload a transformer can
accept. For a tx that can accept a 120% overload, the
current is 315A.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / pravin
Actually it depends upon designer. If we asked designer to
designed for 125% overload, he will provide cooling per
current loading on 125% overload to restrict Hot Spot Temp.
of the winding & Top oil temp. respective to max. ambient
temp.
In this case, we can provide loading of 437A in
terms of ampere on top rating with Hot spot temp & top oil
temp in control on top rating. Actually transformer has
three rating OA/FA/FA. If this transformer is OA/FA/FA then
we can provide this loading.
If it is self cooled then 263A is max. loading.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / sunil kumar das
above answer is also correct.we can put less than full
load current.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / jayant subhash golait
If the word rated current comes,then it is actually safe n maximum permissible limit....Obviously,the machine will misbehave when crossed this limit...to save the machine or to avoid failures,extra cooling may be required that is also within tolerable range...again the manufacturer may declare that value as a rated current which is itself little bit away from tripping or breakdown or danger zone of tolerance....finally ,it is solely depend upon manufacturer n in turn the quality of raw material used to design the machine....
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / narayanan surendran
The question did not talk about cooling and Tap Changer Type.
If over loaded, voltage drop and over heating may occur.
Therefore given rated current 263 A is correct.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sam
That depends on the rated output's power factor and the
load power factor.
| Is This Answer Correct ? | 2 Yes | 3 No |
fog produced due to?
What are the weight of 800KV DA,DB and DC type tower ?
How do I calculate/select Droop CT ratio for various capacity of generators?
In a star-star connected h.t transformer why we use NGR on the secondary (l.t)side.
electricity board have asked me what size meter i need fitted in my garage, its a 415volt supply and i want to run six 20amp supplies tolifts and things plus ten florry lights , what kva meter do i need??
why dc supply is given to the field of alternator
what is the earth resistance
why square root 2 is multiplied with line voltage in selection of LA ie 11/sqrtroot3=6.35 kv and it is multiplied with sqrt2 ie 6.35 KV*sqrt2=8.9 kv we will select 9kv.my question is why we are multiplying with sqrt 2?
what is the slip of synchronous motor
What is the exact load current needed for a place which has 100nos of bulb of each 100w?
how can get electrical "c" licence.i am complited in DEEE.PASSING YEAR OF 1993.WORKING IN PVT COCERN LT LINE.PLEASE ADVISE ME .CELL NO 9994786021
why corona loss is less with negative polarity?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)