i am confused about generator.
i have generator of 380 KVA that is 304 KW by that formula
KW=KVA*0.8...
then by this formula I=KW/V*1.732*0.8 the amperes are 528.673.
so that is the load which i put on one phase of generator or
this is total 3 phase load on Generator.......
Answers were Sorted based on User's Feedback
Answer / sheikh
in single phase distribution system every one phase have to
bear 528Amp with neutral. in 3phase distribution system the
sum of current with phase to phase will be 528amps.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sheikh
in usage of single phase supply every one phase have to given
528 amperes . in 3 phase distribution the sum of current
will be same as 528 amps.
Is This Answer Correct ? | 0 Yes | 0 No |
Thanx alot sheikh... :)
but still one thing i ask u to plz tell me.....
if we run 3phase motors at this generator then maximun load
on generator is 528??
and if yes then we can say that the load on one phase is
528/3=176 amp ???
one more thing plz tell me the maximum load of generator 400
KV.A if we use it for 3phase motors...voltage 400v...
this load plz tell me in amps and also in watts....plzz its
urgentt plzzzz mann....i will be thankfull to u :)
Is This Answer Correct ? | 0 Yes | 0 No |
What quedtion to ask a electrical maintenance technician?
5 Answers Bhel, Royal Furnishers,
Post possible questions for Power Factor Panel FAT / SAT
If stator & rotor of a 3-phase induction motor have different no. of poles, will the motor run or not??
sir, Two different rating of generator going to connect parallel, can it set same DROOP or different. Why? Please explain
PLS SEND THE RRB CHENNAI MODEL QUESTION PAPER my email id is ganesan98655@rediffmail.com
What would be the ratio of a Delta-Wye tranformer having 48000 volts phase to phase on the primary and 4160 volts phase to phase on the secondary?
how to calculate ups and battery rating
hw to find transformer is in normal position? whether its in charged condition or not? except humming sound?
why all selected supply voltage are multiple of 11
Which of the following loss varies with the load A hystresis loss B eddy current loss C copper loss D core loss
What is Faraday's law
what is saturation kit?which use above 15 kw motors panel side.