Answer / guest
DOL-Direct on line Starter, here the starting current will
be 6 times of full load current. A bimetallic thermal
overload relay provides protection against the over load.
There will be no reduction of starting torque during
starting.
Star Delta Starter:In order to limit the starting current
of motors this method is followed. Initially motor windings
are connected in star configuration. The applied voltage
across the winding is reduced 1/1.73 times of rated voltage
due to reduced the voltage current also reduced. Once the
motor reaches the rated speed windings are connected in
Delta. There is 66% reduction in starting toque
Auto Transformer Starters:
In this method windings of the motor is permanently
connected in delta. Reduced starting current is achieved by
applying reduced voltage by means of an auto transformer
while starting, The tapping of auto transformer will be
60%,70%,80% after attaining full speed of the auto
transformer is bypass from the circuit and full system
voltage is applied to the winding, there is a proportional
reduction in starting torque depending upon the taping
selected.
Soft Starter :
Soft starters are Thyristor Drives The rms value of
theapplied voltage is reduced by controlling the firing
angle of power Thyristor. The achieving the full speed
Thyristor conducts in full. Here the starting voltage can
be varied from Zero to maximum value and the motor starting
is vary smooth. Similarly soft-stop facility is also
available therby the motor can be stopped by gradually
reducing the speed.
VFD or VSD:
In VFDs the 50Hz AC is rectified into DC and again inverted
as variable frequency supply , the variable frequency is
achieved by thyristor controlled inverter.
the frequency can be varied from 0-200% This makes speed
contol possible in squrrel cage induction motor. At maximum
frequency the voltage will be eaual to maximum supply
voltage
| Is This Answer Correct ? | 49 Yes | 3 No |
Answer / vinod
dol--direct online starter.a contactor is connected across
the phase during the start.here the current will be more
VSD--VARIABLE SPEED DRIVE--they are actually used for speed
control.in some places they are used for starting
purpose,because the acleration can be programmed
s/s: they are made up of thyristors.each block prosuces a
modulated step by step input
a/t--they are also called as variac.the voltage can be
increased gradually through a cap.
| Is This Answer Correct ? | 44 Yes | 5 No |
HOW VFD USED IN ENERGY SAVING
How many types are using in 220kv/400 kv swith yard
what is the procedure for cable sizing or on what basis we will calculate the size of cable?????
What is core CT & it's function?
Please give me a erda placement paper
What are the advantages of a three-phase system over a single-phase system?
as per standards how many neutral earthings and body earthings are needed.please help me
kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased
How is a 100 MVA transformer cooled?
do we people experience any shock if we catch any one of the three phases (R Y B)in air with out touching ground.
why earth fault current is always less than the o/c
Difference between Profibus DP/PA?what does it stand for and how is it use in process?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)