where we sense the fault from the transmission lines?any
operation example for distance relay?rear panel connection
for this relay?
Answer / k.prakashchandra
The voltage and current measurements are fed to distance
relay.Z=V/I.During fault V decreases and I increases. Then
value of Z decreases.The relay is set to trip for a certain
low value of Z.So the relay does not trip at zero current
but at zero voltage.Connections are to be done as per the
instructions.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is difference between unity power factor wattmeter and upper power factor wattmeter? In short circuit test of transformer the wattmeter used is unity power factor type or upper power factor type wattmeter?
0 Answers Jindal Steel and Power,
suppose a fan is running with phase and neutral. if its neural is touched to body. then fan get stopped. if this fan is connected to phase and ground supply..then why it runs?
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
What is the current carrying capacity of 1.5 rm and 2.5 rm cable
why we use MV panels??? what's r all the needs
practicalLY what is impedence ...?
how can we check a fully charged battery?
I have 2 transformers in two different plants, both are without OLTC but i am facing problem of voltage fluctuation at LV side from only one transformer. i have to change its taps manually twice in a day. Another transformer delivering voltage is ok. Please guide me about the problem
what is the healthy specific gravity of lead acid battery used in DG sets ?
3 Answers Bhushan Power Steel,
how to calculate the megger values for motor, cables and transformers?
How to Calculate Transformer Earthing Electrode Rod Size both Body and neutral Earthing ? Any Standard Formula? Please Suggted
sir,in our plant we r using SATEC PM172E power reading meeters in HT panel side it is monitoring the MB data smart viewer(sever).but last one week we did not get readings inthe server only available in meeter.tell me how communicate meter and server. and also what steps we take for checking.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)