check list of maintenance of transformer?
Answers were Sorted based on User's Feedback
Answer / mohamed fazil
1. check cooling system of transformer and its control circuit.
2. Bushing are cleaned by soft cotton cloth.
3. Take oil sample in drain valve and send its to testing like BDV, Moisture content test,acidity test.
4. Check buchholz relay and its switches(trip switch and float switch).
5. All the terminal boxes should be cleaned.
6.Check oil leakage in transformer and rectify its.
7. Control panels (r&c, RTCC) to be cleaned.
8. Winding resistance check.
9. Insulation resistance check.
10. DGA test carried out in above 132kV transformer for 1 year and below 132kV for two years.
Is This Answer Correct ? | 1 Yes | 0 No |
AVR is used for the Voltage regulation of the Generator using the feedback signal by exciting the field winding of the generator.But how the field winding will be excited & using what?
different between grounding & earthing?
How many percent of power are not being registered if we bypass one side of the meter base terminal using #8 cu wire on 1-phase kwhr meter.
How much ph is maintained of water resistance starter for slipring induction motor ?
What are all the points to be checked for a newly re-winded motor before installation
what should be the value of proper neutral earthing resistance?
What is notching in dc machine?
A 100 KW GENERATOR , only 50 kw load is connected then how much power generated by generator
is it possible to test of bus bar in high rise building without completed full floor ?
Whet is IGBT.How it teste
3phase lt motor winding how to checking with megger
Working of furnace in detail...?