WHY WE USE 4-20mA
Answers were Sorted based on User's Feedback
Answer / sunil kumar
Before using 4 - 20 mA all most of the instruments were
using 0 - 20 mA but after some problem faced for
finding "live zero", it was changed to 4 - 20 mA. By live
zero I mean when the instrument is connected but with 0
process value, the current is 0 mA, & the same current
value is seen when there is a cable damage or no power. By
this it was difficult to find the live zero. After that it
was changed to 4 - 20 mA. 4 - 20 mA Why? why not 5 to 20 mA?
The reason is that most of the a to d convertor which is
capable of providing 1 - 5 VDC with 250 ohms the same
current could be used as per below.
4 X 250 = 1 V DC & 20 X 250 = 5 V DC.
| Is This Answer Correct ? | 78 Yes | 8 No |
Answer / gurpreet chahal
we use 4-20 ma to achieving maximum linearity ,and another
tning safety point of view no spark can genrate up to 20 ma.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / therion
for eg. if we are monitor a flow tube and measure the rate
of flow through the tube or pipe then 4mA will represent
ZERO flow and 20mA maximum flow..if it drops to below 4mA
then it shows reverse flow (which is not good)
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / sandeep bisen
due to achieving maximum linearity in between 4- 20 ma.
| Is This Answer Correct ? | 9 Yes | 11 No |
actually for plc and for electronic systems we usually
supply in mamps. GENERALLLY FROM TRANDUCER WE USE TO TAKE
OP IN 4-20MA , for RTD also .
| Is This Answer Correct ? | 4 Yes | 9 No |
What are the limitations of Kirchoff's laws?
What is the functaion of IGBT in UPS system?
What is the role of Dedicated earthing in UPS System?
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
what is the difference between dry and wet type of 132kV terminations. which one is durable
how can we check a fully charged battery?
6 Answers BEML, Singareni Collieries,
is that any software calculator to calculate the size of cable
cable tray sizing & selection
How to test Alternator stability test for REF relay
Do you need any help with FEWA Electrical Supervisor exams?
The Frequency is measured by _________ bridge ?
in ct secondary one terminal is connected to earth why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)