why 4-20 mA signal is preferred over a 0-10V signal
Answers were Sorted based on User's Feedback
Answer / satishpatel
the signal are transmitted from the field to the
controlroom and vseversa through cables. for long
transmission the cable resistance increases.thus if 0-10v
are transmitted over this long distance,due to the
resistance of cable there will be drop in the voltage and
the signal received at the controlroom will not be
accurate. to overcome this difficulty 4-20ma signal is used
for transmission.
| Is This Answer Correct ? | 286 Yes | 24 No |
Answer / ibrahim s
4-20mA :-
1. Easy to find the open circuit.
2. Less noise interference.
3. Current measures remain same in any point of the signal
line.
0-10V :-
This not able to fulfill the above criteria.
So that 4-20mA is preferred over 0-10v
| Is This Answer Correct ? | 115 Yes | 10 No |
Answer / supratim samanta
If 0-10 mA is used instead of 4-20mA then there will be
difficulties in error detection.Such as if there is any
fault is the transmission lines..we will never know,wheather
the indicated 0mA current corresponds to the initial
value(calibrated) of the measurement or it is due to fault
in transmission lines.
| Is This Answer Correct ? | 120 Yes | 24 No |
Answer / ibrahim s
0-10V :-
1. Voltage droup occurs.
2. Not able to find open circuit(Normally the circuit in
open condition o/p is "0", In 0-10V signal level starts
from 0V itself, so that can not able to find open circuit
easily)
3. Noise interference is high.
4-20mA :-
1. Easy to find the open circuit(because this signal level
starts from 4mA, if the circuit in open the output shows
0mA, so we can find easily the open circuit) .
2. Less noise interference.
3. Current measures remain same in any point of the signal
line.
So that 4-20mA is preferred over 0-10v
| Is This Answer Correct ? | 86 Yes | 7 No |
Answer / banibrata
In case of voltage transmission(here 0-10V)
1.there will be voltage drop along the transmission wire.
2.if we use 0 volt then we will be unable to find whether
the obtained 0 volt output is really the system output or
its due to instrument error.So for "live zero" concept we
need to give a particular value(other than zero) in the
lower range value.
3.Capacitive and magnetic effect due to voltage
transmission will be more than that in case of current
transmission.
4.2-wire transmission is not compatible with voltage
transmission.
But in case of 4-20 mA signal the above problems are solved.
1.In series transmission same current flows through the
ckt.So no current drop occurs.
2.Here the lower range value is 4 mA.So we can easily
detect after looking at the o/p whether the instrument
error occurs or not.In case of instrument error zero
reading will be shown.
3.2-wire transmission is compatible with it.
| Is This Answer Correct ? | 52 Yes | 5 No |
Answer / a.muthu kumar, vacon
In industry, the distance from controlroom
and the field is too long. If we use 0-10v signal
for feedback means voltagedrop will occur because of the
resistivity. So, 4-20mA is preferred instand of 0-10v
signal.
| Is This Answer Correct ? | 27 Yes | 5 No |
Answer / elsayem
in 4- 20
we can find if the process variables give zero because zero
is indicate 4ma
but in 0 - 10 if the process give zero we can not know
because the signal also 0v
| Is This Answer Correct ? | 22 Yes | 11 No |
Answer / luki satria
4-20mA can be easily detected for find a minimum and maximum
level measurement. in in 0-10 V some noise if we are not
prepared measurement
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / shahaji shelke
To troubleshoot the loop or transmission signals,if voltage
signals is used it is difficult to troubleshoot due to it's
non linear properties as well as it's voltage drop within
the transmission,but due to linear current properties it is
easy to troubleshoot the transmission signal or 4-20 mA
signal.
Due to this the 4-20 mA is used in signal transmission.
| Is This Answer Correct ? | 4 Yes | 0 No |
How to ensure vibration sensor functioning accordingly.With out using an other sensor.
what is full form of NAK?
How to Calibrate Flow Switch in field
Can you tell me how we will select RTD and Thermocouples for Temperature applications. I.e How we will choose accurate one for a specefic operation if both having same ranges
How d.p. Transmitter can be applied to close tank?
In split range control, we will control 2 outputs with time interval. Eg :(with 4-20 ma signal, for 4-12 ma we are operating one control instrument like valve & for 12-20ma we are operating other control instrumet (other valve). If we get a signal of 15ma to first instrument (Valve 1), what will happened to the first valve, and if we get signal above 20 ma to 2 valve what will happened ?
Give Detail information about plc,dcs,and scada system?
what are the programming languages used in dcs
Hi buddies! i am facing a problem and if someone could help me it will be an immense pleasure to me. we have compect logix PLC 1769 2L AO module to Heat @ 52 to 56 Deg C .So if anyone can do please help me out with this problem.I'll be highly grateful.
is motorized valve closed when power shutoff?
what would be the minimum flow rate that we can measure on rotameter..?
why we use npn sensor in vibration monitoring system
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)